Hi
New here and looking for some advice. I have an application where I need to measure pressure at 60bar 320degC on a scaling service.
Normally this would be reasonably straight forward with a impulse line and transmitter mounted lower than tapping point allowing condensate to form and have a low flow purge to keep tapping points open.
However I don't have access to purge water supply but I do have steam.
Has anyone ever done a steam purge before?
New here and looking for some advice. I have an application where I need to measure pressure at 60bar 320degC on a scaling service.
Normally this would be reasonably straight forward with a impulse line and transmitter mounted lower than tapping point allowing condensate to form and have a low flow purge to keep tapping points open.
However I don't have access to purge water supply but I do have steam.
Has anyone ever done a steam purge before?
RE: Steam Purge of Pressure Impulse Lines
We both thought that the 'condensate level remains constant because of the cooling effect of the wet/drop legs' premise is called into question when the impulse lines are no longer dead-headed, but now have live steam flowing through them. There must be some amount of condensate flashing at the water-steam interface. Does the system 'equilibrate' at some stable wet leg condensate level that is reliably constant? Don't know.
And there's an issue of the availability of a purge steam supply pressure higher than the line pressure.
Then there’s the issue of a relatively low-flow constant flow regulator. If a Brooks style integrated constant flow-rotameter is not available at that pressure/temperature (I don't whether one is or is not), then we talked a constant pressure regulator with an restriction orifice or a low-flow (needle?) valve, again, assuming supply steam pressure greater than line pressure.
Some months later he told me that they did not try the steam purge, they went with one of those auto-rodder units to clear the impulse lines. So all I ended up with was a picnic discussion, no answers. Hopefully someone here on the forum knows and can fill you in.
RE: Steam Purge of Pressure Impulse Lines
RE: Steam Purge of Pressure Impulse Lines
I would just treat it as a normal blow-down, drop off the line and go down a few feet then tee off and slope back up into the transmitter with a blow-down valve at the bottom.
When you blow it down the vertical pipe is going to grow in length so the slope up section should be tubing with enough bends in it to compensate for the growth otherwise you might see the tubing pull out of the fittings which would not be nice. You could even replicate a pigtail syphon in the tubing to ensure that the transmitter is not subject to steam temperature,
I would also include a condensate pot to assist in refilling the blow-down with condensate.
Hope this helps