Hi,
I am designing an HFO tank,
Now as you might all know that the HFO needs to be kept at 50C for it to stay in a good state of flowing,
I am calculating the heat loss from the tank,
There is some things that confuses me,
1-how can i calculate the heat loss from the natural vent?
2-how can i estimate the heat loss from the nozzles?
3- is there any design standard that goes through all the estimated calculation?
I am currently using the ABC chemicals methods of estimating the overall heat loss (nozzles and natural vent are excluded) how ever data showed that its accurate.
4-any standard that can guide me through the designing of the steam heating coil?
Best of regards,
I am designing an HFO tank,
Now as you might all know that the HFO needs to be kept at 50C for it to stay in a good state of flowing,
I am calculating the heat loss from the tank,
There is some things that confuses me,
1-how can i calculate the heat loss from the natural vent?
2-how can i estimate the heat loss from the nozzles?
3- is there any design standard that goes through all the estimated calculation?
I am currently using the ABC chemicals methods of estimating the overall heat loss (nozzles and natural vent are excluded) how ever data showed that its accurate.
4-any standard that can guide me through the designing of the steam heating coil?
Best of regards,
Detailing is a hobby,





RE: Steam coil for heating-recommendations
Designing heating coils is rather simple after you know the heat balance. You need to know the characteristics of the (probably fin-tube) heaters, your steam properties and the liquid properties. That mostly gets you the footage of coil needed. Design and locate the coil packs with slope for condensate return, to provide good coverage and to create convective swirls that don't interfere with each other. Coordinate with fill, suction and recirculation piping, air sparging and any blending equipment.
For a quick and most likely successful installation, engage your coil vendor to do the calculations for you. Ask for and follow their recommendations to avoid coking.
My opinion only - remember - you read it on the World's Wild Web !!!
RE: Steam coil for heating-recommendations
Thank you that’s very helpful!
And also when you said “locate the coil packs with slope”, did you mean that the coil should be helical downward attached on the tank shell?
Can you recommend any book?
Detailing is a hobby,
RE: Steam coil for heating-recommendations
RE: Steam coil for heating-recommendations
Thank you again @IFRs
Detailing is a hobby,