The plant I am working consists of a flare and flare has 3 pilots. In-service inspection was carried out with the aid of binocular and flare is burning however I could not notice any flames from pilots. Please suggest is it acceptable and if not what action needs to be taken.
Thanks & regards,
Prathap K
RE: Flare Inspection
If the process logics in the cause and effect matrix indicate that the pilot lines are all left open during normal operation, then see if any one of the following may apply to your case:
a)Pilot may actually be operating with an almost transparent flame ( may actually be blue but looks transparent against a clear sky background).
b) Pilot line pressure may be low and unable to overcome liquid static head in the pilot riser ( pilot gas may be high HC / water dewpoint, resulting in liquid condensation in riser).
If (b) is the case, see if you can drain out the pilot riser at the flare stack base low point drain.
Prathap,
Just wait for a dark night with no full moon and look at the Flare Tip through a strong Telescope.
If you see a Glow (around the Tip) then the Pilot is functioning.
No Problem!
Sometimes its possible to do all the right things and still get bad results
In a standard flare system design there are thermocouples around pilot burners, if pilots are burning they show temp in the range of 350-450 deg C. If this temp drops below 200 deg C then there is high probability that pilot is not burning.
Try to see in the night from a nearby elevated structure (from top of some column or reactor). It will be much clear when process vent to flare is minimum. Now a days some people use drone cameras for online flare tip inspection. Side by side you may check and confirm fuel gas composition used for pilots and check/clean pilot gas supply line strainer taking bypass in line.
Thank you very much for the valuable suggestions. The pilot was functioning properly but was not visible during the day time.
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
White Paper – Data Security and Know-How Protection
Our data is constantly exposed to the danger of being intercepted or stolen as it wends its way over global data networks. Data security measures and measures for protecting intellectual property should not, however, first be implemented when data is exchanged – companies must lay the foundation for these measures within their own organization. Download Now
White Paper – Collaboration in the PLM Context
The influence exerted by the Internet of Things (IoT) means that there is a steadily growing need for collaboration in industry. Partners from new industries and areas of application need to be integrated in cross-company business processes to ensure that the lifecycle of smart, connected products can be managed from end to end. Download Now
White Paper – The Challenges of PLM Collaboration
There is cross-company collaboration - and then there is cross-company collaboration. Large-scale corporations and joint ventures need different mechanisms to protect intellectual property from those required for communication between different company locations with heterogeneous IT landscapes. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close