BMS Chiller Graphic with Heat Balance
darrenyee88
56
I have attached the Chiller graphic and would like to get some advice on how to interpret the data especially heat balance . How do I know this data is correct and not showing any issue to the chiller.
Darren
What issue are you looking for?
Basic checks would be
- if chiller is enabled, is it working - isolation valve open, pump on, it's actually cooling the water, etc
- same as above but for condenser water side
- if multiple chillers are enabled, are they equally sharing the load, or is one chiller providing more chilled water or colder chilled water than another
- if chiller has multiple stages, what %load/power is chiller operating, and does that match up with its cooling output
- are the temperatures you see going in and out of your chiller and cooling tower aligned with what you designed it to do and what your system needs
This is system schematics, not chiller-cycle schematics, and you should make it clear to us what you don't understand.