Hello,
Motor rated power and torque (output) is directly proportional to the square of the voltage. If you use a 460Vac motor on a 400Vac network, it won't be able to develop the "rated torque", and instead, will develop (400/460)^2 = 75.6% of it.
What will happen depends on the mechanical load connected to the motor. Possible scenarios:
1. Motor starting torque is not enough to accelerate the mechanical load => Motor will fail to start (luckily protections will trip)
2. Motor start ok but it cannot develop enough torque to move the mechanical load at the required speed. Probable the motor will trip due to overload
3. Motor start ok and develop enough torque to move the mechanical load (the most unlikely scenario)
Regards,
Juan