Teck Cable for Substations (indoor/outdoor &shielded v grounded)

Teck Cable for Substations (indoor/outdoor &shielded v grounded)

Teck Cable for Substations (indoor/outdoor &shielded v grounded)

(OP)
Hello all,

After talking with one of our commissioning leads. He made the requests that if possible, to use Teck cable for control and power cables as they can strip them with relative ease.

Looking at some catalogs, i can see they come with a grounding conductor but no shield. Which is what i would like to use, and in my experience they work well for protecting against voltage spikes, noise, etc.

I am just wondering if anyone here would have any insight or preference over regular shielded cable (vs Teck) for control cables going from the substation yard into the building and between panels.

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

Teck doesn't provide the best shielding properties for control cables, especially VHF transients (think switches pulling arcs). Concentric copper shielding is best. Looks like a corrugated copper sleeve between the inner and outer sheaths. Also, cable shield needs to be grounded.

Personally, I would not accept Teck for control cables. This often gets suggested by construction crews (easier for them to deal with fewer types of cable), but they have zero insight into the shielding properties.

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

(OP)
Thanks Marks1080.

I am inclined to agree with you.

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

(OP)
hi marks1080,

I asked our supplier at Anixter, apparently

getting shielded cable 14AWG is special order. she wrote:
"Shielded power cables are not used for most other industries until you get into medium voltage cable. Standard stocking teck and tray type cables would be unshielded only in 14AWG and larger. "

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

Interesting. We dictate rather harshly exactly what type of cable we want. We also buy enough of it that they gladly provide it.

Anixter and Shawflex are the same thing right? Because that's where we get a lot of our cable. Ask for M582 spec specifically. I can tell you we have active material for 7C#14AWG cable of this type. I don't like the statment you got saying shielded power cables are not typically used until medium voltages. The cables we buy are rating for 600V so that makes no sense at all - that is 100% bullshit. Shielded cables must be used, especially if you are using IEDs. If you are converting from electromech to IED and all of a sudden you have weird things happening and the only thing you changes was the relay, it almost always means the cable shielding was never properly done. Also, keep in mind the 60HZ noise isn't a problem. It's the 100MHz ++++ noise that damages equipment.

Regarding TECK cable: Do not use this for control circuits. TECK is only for power supplies (typically AC or heavy DC trunks). The drain wire on the teck cable IS NOT RATED to handle transient noise, especially high frequency.

If they offer to send you something with a tape shield do not accept. they are notorious for the shield breaking inside the cable when they are being pulled.



RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

I just checked and it is a special order for us as well.

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

(OP)
Yes Shawflex is bought by Anixter i believe.


For status and alarms i am thinking of usign a 300V instrumentation teck cable with individual and overall shield type ACIC.

but i am having a hrd time finding #10AWG shielded.

i will inquire about that M582. What type of cable do you use for trip coil and close coil?

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

Check out Okonite CLX Type MC cable. It has an extruded continuous aluminum sheath (not interlocked) that provides good shielding and it contains three ground wires in the interstices of the main conductors. #10 control cable in CLX should be a stock item. It will be expensive compared with Teck cable.

RE: Teck Cable for Substations (indoor/outdoor &shielded v grounded)

We use the same cable for Trip/Close circuits.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

eBook - Mastering Tolerances for Machined Parts
When making CNC machined parts, mastering tolerances can be challenging. Are general tolerances good enough? When does it make sense to call out for tighter tolerances? Do you need a better understanding of fits, datums, or GD&T? Learn about these topics and more in Xometry's new e-book. Download Now
eBook – How to Choose the Correct Corrosion Testing Method
When designing a metal component, engineers have to consider how susceptible certain alloys are to corrosion in the final product’s operating environment. In a recent study by NACE (National Association of Corrosion Engineers), it was estimated that the direct and indirect costs of corrosion in the United States is approximately 6.2% of the GDP. In 2016, that cost exceeded $1 trillion dollars for the first time. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close