Power flex 40 hardware over current fault

Power flex 40 hardware over current fault

Power flex 40 hardware over current fault

(OP)
Hi

Can anyone advise?

I have 2 motors which is rated at 0,75 kw each and 3 amp connected in series and a power flex 40 with a 6 amp max current rating.

The current limit setting on the drive is 6A.

The problem that I am experiencing is when the motor starts up to 70% it tripped with an F12 h/w over current fault, I measure the amps to be below 2.5A when it trips, I have replaced the motors and the drive .

Any further ideas

Thank you

RE: Power flex 40 hardware over current fault

Are the motors in series? How did you even do that?

Or, are they in parallel? If so, were the 2.5 A measured at the motor or at the drive? If measured at motor, you may have 5 A in total. So, it should trip.

If you activated autotune with two motors connected, you will get problems. The drive expects one motor in such cases and the outcome could be just about anything. Use autotune only with one motor connected. If you need best dynamic performance - you may need to rethink. If standard performance is OK, then use scalar mode.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

RE: Power flex 40 hardware over current fault

Is parameter A084 [Boost Select] set to option 5?

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Power flex 40 hardware over current fault

(OP)
Thank you for the reply.

The motors are actually connected in parallel

The run boost setting is at 8

We actually found the problem which was on one of the isolators which had water in the junction box. The isolator was blown. Once we replaced the isolator. The reading is now at 1.3A

Thank you very much for your help and insight

RE: Power flex 40 hardware over current fault

So basically, the VFD was finding a fault that you didn't know existed...

They are good at that.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden

RE: Power flex 40 hardware over current fault

Thanks for letting us know. Easy to forget about such things when there are hundreds of parameters and other things to worry about.

Gunnar Englund
www.gke.org
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

White Paper – Choosing the Right Spring Loaded Connector
In today’s cost-sensitive world, designers are often driven to specify the lowest cost solution for every aspect of their designs to ensure that their solution is competitively priced and their company remains profitable. However, specifying a low-cost, low-quality connector solution can result in premature failure, considerable re-work costs and damage to reputations. Download Now
eBook – Own the Lifecycle: Sustainable Business Transformation
Increasingly, product and services companies are seeking more information and control in the operational lifecycle of their products, including service and use. Better information about the operational lifecycle, and the ability to use that information, requires more than just unstructured data flowing back from products in the field. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close