Power flex 40 hardware over current fault
Hi
Can anyone advise?
I have 2 motors which is rated at 0,75 kw each and 3 amp connected in series and a power flex 40 with a 6 amp max current rating.
The current limit setting on the drive is 6A.
The problem that I am experiencing is when the motor starts up to 70% it tripped with an F12 h/w over current fault, I measure the amps to be below 2.5A when it trips, I have replaced the motors and the drive .
Any further ideas
Thank you
RE: Power flex 40 hardware over current fault
Are the motors in series? How did you even do that?
Or, are they in parallel? If so, were the 2.5 A measured at the motor or at the drive? If measured at motor, you may have 5 A in total. So, it should trip.
If you activated autotune with two motors connected, you will get problems. The drive expects one motor in such cases and the outcome could be just about anything. Use autotune only with one motor connected. If you need best dynamic performance - you may need to rethink. If standard performance is OK, then use scalar mode.
Gunnar Englund
www.gke.org
Is parameter A084 [Boost Select] set to option 5?
Bill
"Why not the best?"
Jimmy Carter
Thank you for the reply.
The motors are actually connected in parallel
The run boost setting is at 8
We actually found the problem which was on one of the isolators which had water in the junction box. The isolator was blown. Once we replaced the isolator. The reading is now at 1.3A
Thank you very much for your help and insight
So basically, the VFD was finding a fault that you didn't know existed...
They are good at that.
Thanks for letting us know. Easy to forget about such things when there are hundreds of parameters and other things to worry about.
Gunnar Englund
www.gke.org
Click Here to join Eng-Tips and talk with other members! Already a Member? Login
White Paper - A Guide to 3D Printing Materials
When it comes to using an FDM 3D printer effectively and efficiently, choosing the right material at the right time is essential. This 3D Printing Materials Guide will help give you and your team a basic understanding of some FDM 3D printing polymers and composites, their strengths and weaknesses, and when to use them. Download Now
Close Box
Join Eng-Tips® Today!
Join Us             Close