using 12/20kv cable on 3.3kv system voltage

Status
Not open for further replies.

Olop

Electrical
Joined
Jan 13, 2019
Messages
2
Location
ID
could we use 12/20kv (24kv) cable to replace 3.6/6kv (7.2kv) cable in 3.3kv system voltage? what is the standard reference?
 
Theoretically speaking it is possible. However it depends on application-as current carrying capacity, armouring, earthing, bending radius, reduced smoke and other.
1.8/3.3 see BS 5467 and for 12/20 IEC 60502-2.
 
@7anoter4, the cable size is the same 3x185mm2, since the market availability (due to minimum length purchased) is only the 12/20kv despite of requirement 3.6/6kv. Thank for the feedback.
 