I've got a distribution system in a pumping plant that will utilize a PLC to control two pumps supplying water to a number of users. The pumps will draw water from a reservoir(river) and supply the distribution ring.
Should the controls system be based on the characteristics of the system(load profile)? The way I see it, if there is a constant demand for water, it would make sense to maintain flow in order to level out the pressure in the system and avoid pressure drop, say when a valve is opened. If the demand is low and has a discrete (step function) characteristic thoughout the day, then perhaps it would be better to maintain pressure in the piping and not care about flow? This would minimize run time of the VFD as well, it there is no demand for 6 hours, the VFD would pressurize the system piping and shut off; check valve would prevent water from flowing back into the pit.
Currently there is no discharge back into the reservoir, but we may add a valve to "dump" excess flow essentially back into the reservoir if we elect to maintain a minimum flow in the system. To me, it would be wasteful to maintain a minimum flow for low demand system.
My background is not Mechanical, but am curious if I'm on the right path approaching the design criteria.