I'am actually a Entry Level BLDG Inspector and I've been presented w/ a Contractor who has completely gusseted some flat roof trusses which have been damaged in a fire resulting in a negative camber of at least 4", he has jacked up the trusses and applied 7/16' OSB across the entire span of the flat truss, My concern is: has the excessive rigidity imposed on the required deflection enough that the load transfer has gone from Vertical to a Lateral Shear imposing on the exterior walls?
RE: Gusseting flat trusses w/ OSB
If it was my problem, I'd insist on the involvement of a professional engineer. Get a report and an approval/disapproval.
RE: Gusseting flat trusses w/ OSB
RE: Gusseting flat trusses w/ OSB
Review your applicable code to understand how this works. In the UBC or IBC, Chapter 17 governs in-situ load tests. (see 1713 in the IBC 2000)
So basically, you can request that the contractor hire a structural engineer to validate the new "design" through calculations and his certification ... OR ... you should request that the contractor perform a load test to verify that he indeed meets the load carrying capability that is required.
Anything else would be putting the public at risk.
RE: Gusseting flat trusses w/ OSB
1.) Although I have not had the opportunity to investigate such a case, the American Plywood Association provides a clear step by step guideline for the calculations for plywood gusseted box beams. Worth looking into.
2.) Perhaps we are overlooking a consideration that may be more important: The deflection in the middle of the trusses might prevent proper drainage of the rainwater on the roof.
RE: Gusseting flat trusses w/ OSB
Keep in mind that firemen have their own opinions regarding what they like, or don't like in construction techniques.