Hi Veritas,
I think that you will find that there is no 'magical' cancellation of harmonics in the 20 x 4kW ASD scenario vs a single 80kW ASD.
The only way to cancel any of the harmonic currents is to say move half (ie 10)of the 4kW ASDs over a 30 degree phase shifting transformer (ie delta-delta) and essentially make a twelve-pulse drive (at least as far as the power system is concerned).
Otherwise if you truly have a harmonic issue, you could possible solve this by applying either passive or active harmonic filters.