ETABS Pier Wall Forces: Why does Shear 22 vary over story height?
NathanNZ
NZ
I have a 3 storey building with ground floor RC walls and concrete first floor, above first, second floor and roof is and steel and timber frame. I am designing the ground floor concrete shear walls using the demands outputted from ETABS. I have used manual seismic loads applied to the centre of mass of the first floor diaphragm. Each wall has been drawn separately with no spandrel panels over windows for simplicity. I have assigned each individual wall as it's own pier label.
When I view the pier force diagrams, I get the expected moment 33 diagram (triangle shape) starting from zero at the top to a base moment (linearly increasing) therefore I would expect the Shear 22 diagram to be constant. However I get linear varying shear force diagram sometimes starting negative at the top and changing to positive at the bottom.
I have uploaded a pdf with M33 and S22 diagrams for the one of the seismic cases. This is not a max/min case so loads should match up.
At this stage, I am considering outputting the base moments (M33) to excel and manually calculating the shear (S22) for each wall. Shear = Base Moment / Height (3.4m)
Any idea why this is happening?
 https://files.engineering.com/getfile.aspx?folder=96bdc61d-d386-4d77-9cab-82ba55c3569c&file=etabs_pier_force_query.pdf
What type of analysis are you doing? Modal/response spectrum? Using the standard solver are there any instabilities noted in the analysis log?
Yes, seems to be an issue with stability of the model. I ran the standard solver which gave joint error: diag = 0, a problem with zero stiffness. It was occurring to the all the joints at the top of the walls. The problem was I had tried edge releasing the walls out of plane which was causing the issue. I was running a linear static, using user inputted seismic loads.
Attached are correct results. I have showed the original results to show what difference it makes and why instability results needs to be resolved.
 https://files.engineering.com/getfile.aspx?folder=0cba4f2b-c788-442a-81d4-3a68fd5e0513&file=etabs_pier_force_solved.pdf