Custom Shear Wall Panel
phamENG
Good morning. I'm attempting to model wood shear walls using ZIP WALL R-6 insulated sheathing panels. For those who aren't familiar, this type of wall system consists of a wood structural panel with rigid insulation adhered to the inside face (between the panel and the studs). They come with a third party testing certification and diaphragm/shear wall design tables analogous to those in the NDS. They aren't great for shear walls - they aren't quite as strong as an OSB or plywood wall, and because of the placement of the insulation they are actually more flexible than a wall sheathed in nothing but GWB. This is in a moderate wind, low seismic area, single story building so the flexibility isn't a deal breaker. I'm just trying to figure out how to get the strength and stiffness data from the testing group into RISA so I can transfer the loads to the foundation framing (the structure is elevated on an open foundation) with some level of accuracy. Any help would be appreciated. Thanks.
 https://files.engineering.com/getfile.aspx?folder=9695f8d5-f9c1-4a44-abca-f107688f744f&file=E1561_R0482_Huber_Engineered_Woods_LLC.PDF
If you've installed into C:\Program Files\RISA, then in your Documents folder there will be a subfolder called "\RISA\ Wood Schedules\ShearPanels\". This will have a bunch of XML files which contain the wood panel properties from the NDS tables. These files can be edited in Excel.
Outstanding. I'll give it a try this afternoon. Thank you, sir!