Oct 16, 2018 #1 TittyThomas Electrical Joined Oct 15, 2018 Messages 2 Location AU Dear Engineers, How can we test vector shift with omicron if three phase voltages are connected to relay. Regards
Dear Engineers, How can we test vector shift with omicron if three phase voltages are connected to relay. Regards
Oct 16, 2018 Thread starter #2 TittyThomas Electrical Joined Oct 15, 2018 Messages 2 Location AU How to test Loss of Mains? Upvote 0 Downvote
Oct 16, 2018 #3 DTR2011 Electrical Joined Oct 12, 2006 Messages 682 Location US Omicron has a template in the registered user area for a ROCOF relay that also includes Vector shift. DEA Interconnection G59 PTT This PTT enables the user to test relays according to G59 Engineering Recommendation (ena Sept. 2015). Upvote 0 Downvote
Omicron has a template in the registered user area for a ROCOF relay that also includes Vector shift. DEA Interconnection G59 PTT This PTT enables the user to test relays according to G59 Engineering Recommendation (ena Sept. 2015).