I'm trying to design pressurization system for stairwell.actually, We follow IBC AND ASHRAE IN WHICH I can not find and specific number of doors to be open while designing the system to calculate the pressurization fan capacity.My question is regarding the open door airflow.I have seen many engineers design the system so that the airflow velocity through the open door is around .75 m/s to hold smoke back from entering the stairwell which would increase the fan capacity to meet this demand.But i can not find such a criteria in Ashrae at all.A solved example of pressurization system using Contam software shows that, it is only enough to have a positive pressure difference across open door to guarantee that smoke is held back from entering the stairwell.Am i getting it right? because i'm confused.

Thanks in advance

RE: Stair pressurization with open doors

Go for zero doors open.

If you do, you'll have a well designed stair pressurization system that maintains the .10 to .35 range that you need. For a typical 7-15 floor building, it might be a 5000-7000 cfm unit.

When you design for 1 door open (about 21 ft2 of leakage plus normal construction leakage) or 2 doors open (about 42 ft2 of leakage added to construction leakage) your 7,000 cfm fan turns into a 30,000 or 40,000 cfm fan. With quite a bit of HP difference.

In essence, no. Don't try to size fans based on open stair doors. If any AHJ wants you to do otherwise, they need to go to ChasBean1 school..

RE: Stair pressurization with open doors

I used 2 doors open. Foolish to think about saving money when lives could be at stake. Use constant speed fan but with bypass damper to exhaust or recirculate air, controlled by stairwell pressure sensor.

RE: Stair pressurization with open doors

But if pressurization is too high, can any stairwell door be opened for evacuation?

RE: Stair pressurization with open doors

Chicopee, that's the reason for the upper limit of .35". When you start to approach ~.3", doors that lead into stairwells start to exceed 30 lbf (life safety code) door opening force.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources

White Paper – Your Construction ERP RFP Checklist
Selecting business software for a medium to enterprise-sized construction concern is extremely challenging in large part because most enterprise resource planning (ERP) suites originated in the world of repetitive manufacturing and are therefore a poor fit for a project and asset-centric business. However, midsize to large contractors need the predictable, auditable processes that ERP delivers. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close