Sep 19, 2018 #1 Zeke Civil/Environmental Joined Jun 5, 2001 Messages 9 Location US A contractor placed a 3" schedule 40 NEMA pipe in a column for the drainage system. The specs call for ASTM D1785. Will this be a problem? What concerns would the client have with this type of error?
A contractor placed a 3" schedule 40 NEMA pipe in a column for the drainage system. The specs call for ASTM D1785. Will this be a problem? What concerns would the client have with this type of error?
Oct 22, 2018 #2 amlinerrichard Civil/Environmental Joined Feb 16, 2015 Messages 66 Location US Compare the 2 ASTM's to see if the pipes are equal. Upvote 0 Downvote
Nov 5, 2018 #3 bridgebuster Active member Joined Jun 27, 1999 Messages 3,970 Location US D1785 is considered a pressure pipe whereas NEMA is a conduit for wiring. Dimensionally they're both the same. Upvote 0 Downvote
D1785 is considered a pressure pipe whereas NEMA is a conduit for wiring. Dimensionally they're both the same.