we are having two self actuated pressure regulators on LPG Line to plant having inlet pressure of 270psig and set pressure of 14.7 psig.
the capacity of each regulator is 230kg/hr of lpg.however it was learnt that the capacity should have been 315kg/hr of LPG for each regulator.
these regulaors have been procured and installed at site.
now question is how to ensure that these regulators provide 315 kg/hr of LPG in place of 230kg/hr?
or a third regulator in pararllel is the only answer?
the capacity of each regulator is 230kg/hr of lpg.however it was learnt that the capacity should have been 315kg/hr of LPG for each regulator.
these regulaors have been procured and installed at site.
now question is how to ensure that these regulators provide 315 kg/hr of LPG in place of 230kg/hr?
or a third regulator in pararllel is the only answer?
RE: self actuated pressure regulators
RE: self actuated pressure regulators
You want to increase the flow by 37% I expect that would cause a significant drop in pressure, only the designer of vendor can tell you if it's possible without more detail.
Regulators with a pilot regulator (small regulator controlling a larger valve) tend to have better flow characteristics because it acts similar to a pressure amplifier