11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

(OP)
Is it mandatory to provide boot for 6.6kV (HV) terminals to certify the enclosure as Ex ‘e’?

Or

the junction box containing bare (exposed) live terminals inside the junction box can be certified for use as Ex ’e’ enclosure?

My concern is some static discharge during the switching of connected long length cable (about say 4 kms).

Can anyone share the experience or give some literatures on this?

RE: 11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

Hi krisys

Are you a manufacturer of such a box, or are you an end user?

Are you working to IECEx regulations or some other system?

If you are working to IECEx regulations, and you are a manufacturer, then you really need to review 60079.7 which specifies requriements for Ex e certification.

Even if you are an end user, I would review 60079.7 for information. I would have had a look at it myself for you but I do not have my copy handy.

That being said, there are certified Ex e terminals for high voltages out there which do not specify a boot or similar. However most I have seen include significant barriers/shrouds around the terminal. Remember the terminal itself needs to have certification, in addition to the Ex e box. As long as you comply with the requirements of those two certifications then your installation meets Ex e.

But also refer 60079.7 for reference.


RE: 11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

(OP)
MB

Many thanks for your feedback. If you can tell me which section, it would be helpful. Nevertheless, I will refer IEC 60079.7. I will also share my own interpretations/understanding of this standard.

Just for information, I am an end user. For the offshore application.

Someone said to me that IEC 60079 is for the low voltage. For high voltage it may not be fully applicable. Would you throw some light on this as well?

RE: 11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

Hi Krisys,

It is not correct that IEC 60079 series of standards apply only to low voltage equipment.

See excerpt from IEC 60079-7 below.



This is just a snippet, there is probably more in that standard that applies to your application.

Regards,

Michael.


RE: 11 kV Ex 'e' certified junction box having exposed connectioninisde the enclosure

(OP)
Thanks Micheal
This is very useful.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close