Shear Lug concrete breakout

Shear Lug concrete breakout

Shear Lug concrete breakout

(OP)
Hi
I am sizing the shear lug for seismic forces. I have a situation where pier is shallow. The 45 degree failure plane for concrete breakout of shear lug is controlled by height of pier. The amount of concrete area available for breakout is not sufficient to resist shear. I am adding a shear wall on both sides of the pier with width greater than the width of the shear lug. If I do this, I don’t need to check the concrete break out of shear correct as there is no free edge. Correct? Shear is transferred by bearing only correct?

RE: Shear Lug concrete breakout

Sounds right to me.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Shear Lug concrete breakout

(OP)
ok Thanks

RE: Shear Lug concrete breakout

(OP)
With continuation of the above query, do I need to pay any special attention to pier wall interface design? The force is around 500kips. I am designing the wall as a shear wall with min horizontal and vertical reinforcement as per code and for the 500kips force.

RE: Shear Lug concrete breakout

There may be a fair bit to consider:

- bearing / bursting / load spread.
- potential for wall buckling.
- shear transfer from wall into soil, SOG, or neighboring foundations.

To get into specifics, we'd need to take a look at the specifics of your situation in plan and elevation.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

RE: Shear Lug concrete breakout

(OP)
The pier is 3'x3' and the wall attaching to it is 2' wide. The shear lug is 1' wide.

- Bearing/Load spread: This should not be a problem as wall is 6'' bigger on either side of the lug.
- The wall is 1' wide and 5' tall. I dont think wall bucking will be an issue. Will look into it.
- Shear transfer from wall to the spread footing is transferred through the longitudinal bar friction extending into the footing.

The pier and the wall is modelled in FEM. Horizontal bars between pier and wall are provided per FEM model.

I have been trying to upload a pic but never works.

RE: Shear Lug concrete breakout

Still hard to visualize but, based on your description, nothing's jumping out at me as a deal breaker.

I like to debate structural engineering theory -- a lot. If I challenge you on something, know that I'm doing so because I respect your opinion enough to either change it or adopt it.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close