Application of anti-condensation heater for a 6.6kV Junction Box
Application of anti-condensation heater for a 6.6kV Junction Box
(OP)
I have to procure some outdoor power Junction Boxes (JB) to be used in the offshore oil producing platforms. The purpose is to provide a junction point between the subsea composite cable and the above sea 6.6kV and Fiber Optic (FO) cables. The location of installation is classified as hazardous area.
This installation will be in the Middle Eastern region, where the ambient temperature goes above 50 deg C in the summer with close to 100% humidity.
I am specifying the junction box suitable for the hazardous area Ex 'e' type and IP56 enclosure. Also I have specified the requirement of breather. The volume of the box is about 0.4525 cubic meter. Now, my query is that whether I need to specify space heater (anti-condensation heater) for the junction box?
Also I would appreciate if someone enlightens me on what is the criteria to specify the space heater.
Any industry standard available for reference on this subject?
Also a question regarding the breather:
Will the breather prevent the moisture entry? or it will only restrict the free air movement.
This installation will be in the Middle Eastern region, where the ambient temperature goes above 50 deg C in the summer with close to 100% humidity.
I am specifying the junction box suitable for the hazardous area Ex 'e' type and IP56 enclosure. Also I have specified the requirement of breather. The volume of the box is about 0.4525 cubic meter. Now, my query is that whether I need to specify space heater (anti-condensation heater) for the junction box?
Also I would appreciate if someone enlightens me on what is the criteria to specify the space heater.
Any industry standard available for reference on this subject?
Also a question regarding the breather:
Will the breather prevent the moisture entry? or it will only restrict the free air movement.
RE: Application of anti-condensation heater for a 6.6kV Junction Box
I have recently designed an enclosure for installation on an offshore oil rig. The customer had a very, very detailed design guide. Perhaps your customer has one too. Trial and error is the wrong way to learn safety.
You can buy breather desiccators. I have used these on otherwise sealed airborne systems.
You need a heater at 50°C?
--
JHG
RE: Application of anti-condensation heater for a 6.6kV Junction Box
When the RH is high, a rise in ambient temperature may leave the temperature of internal components below the dew point.
This will cause instant condensation, even at high temperatures.
The core iron of halted motors and generators is particularly susceptible, even at elevated temperatures
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: Application of anti-condensation heater for a 6.6kV Junction Box
ElectroMechanical Product Development
(aka Electronic Packaging)
UMD 1984