Voltage Regulators in Series in Power Distribution System

Voltage Regulators in Series in Power Distribution System

Voltage Regulators in Series in Power Distribution System

(OP)
Hi. Can anyone comment on experience with using multiple Voltage Regulators in series on a distribution network, for example in maintain voltage on a long overhead line. Would there be issues with power factor towards the end of the line because of the impedance of the regulators in series? If so how is this overcome, it is my understanding that in the US for example where there are several miles of overhead line distribution they use many of these in succession to maintain the voltage at distribution level.

Thanks

RE: Voltage Regulators in Series in Power Distribution System

They also install line capacitors for voltage control. Both fixed and switched capacitors.

RE: Voltage Regulators in Series in Power Distribution System

The power factor at the end of the line will depend on the power factor of the load at the end of the line, not on series impedance of the line.

Quote (OP)

distribution they use many of these in succession to maintain the voltage at distribution level.
More accurate to say;
"They may use more than one of these in succession."

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Voltage Regulators in Series in Power Distribution System

(OP)
Hi.

But the impedance of the regulator/s would be present if I had the equivalent model from source to load and via the return path, doesn't the inductance of the regulator (just coils same as a transformer) create a phase shift and hence affect the power factor?

Thanks

RE: Voltage Regulators in Series in Power Distribution System

Transformer phase shift affects both current and voltage, has essentially zero affect on power factor.

RE: Voltage Regulators in Series in Power Distribution System

(OP)
Hi.

Interesting you say that. Last I checked a large inductance (ie a transformer) causes the current to lag the voltage.

Thanks

RE: Voltage Regulators in Series in Power Distribution System

A transformer and a reactor are rather different things, even if they both have coils of conductor around a core.

RE: Voltage Regulators in Series in Power Distribution System

True enough, David; but as an inductive device a transformer does absorb reactive power, which it will draw from the source in the same manner as any other inductive load.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Voltage Regulators in Series in Power Distribution System

Second or third order effect, sure. Consider a delta-wye transformer, with a phase shift equal to some odd multiple of 30 degrees; apply metering on both sides. The metering will show approximately the same power factor on each side; nothing like a 30 degree change in power angle. The magnetizing branch of the transformer is a shunt load and does have a power factor other than unity. But it will be the load external to the transformer that determines the power factor of the flow through the transformer.

RE: Voltage Regulators in Series in Power Distribution System

Similar to how when placing MW load on a generator excitation has to be increased to compensate for internal drop, otherwise VAR absorption will commence.

CR

"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]

RE: Voltage Regulators in Series in Power Distribution System

Hi Cerkit,
I have seen three in a row, from distant memory it was a 180 km 22 kV line with a MW or two of total load.
The source power factor is changed only marginally, since the series impedance of regulators is small (zero at nominal tap, often only a percent or two on nameplate base at extreme tap) and the shunt impedance large relative to load impedance.
Utilities often have a rule specifying a maximum number in a row, but nobody has yet explained to me the basis for these rules.
Usually they are time-graded, so the more in a row, the slower the response and in extreme cases lamp flicker or step voltage change limits may impose a constraint on the number in series. Other than this it seems to be based around "That's the rule" with no technical justification.
John.

RE: Voltage Regulators in Series in Power Distribution System

Voltage regulators used on long rural lines with predominantly single phase loads may experience a neutral shift. While the phase to neutral voltages are correct, the line to line voltages and the phase angles may become unequal.
This is no problem for single phase loads but reduces the available HP of three phase motors.
In extreme cases the motor current at no load may exceed rated full load current.
When regulators are in series, it is possible for one regulator the correct the neutral shift of another series regulator but the odds against this are overwhelming.

Bill
--------------------
"Why not the best?"
Jimmy Carter

RE: Voltage Regulators in Series in Power Distribution System

The series impedance of a regulator is quite small, perhaps equivalent to a few hundred feet of overhead conductor. The losses in a regulator are mostly reactive, so the regulator would have a slight impact on power factor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close