Extremely unusual distribution system pressure drop
6

Extremely unusual distribution system pressure drop

Extremely unusual distribution system pressure drop

(OP)
I work for a water utility and we have a conundrum that none of us can figure out. One of our zones is a pump station/water tank fed setup where water going to the distribution system is controlled by tank level. While a typical setup would consist of a pump station being tripped on and off by tank level, our setup is a bit different and I'll try to explain as best as I can as follows:

We have a VFD pump station which maintains a constant pressure our water plant that provides both plant water and serves a portion of our system by filling a reservoir. The pump station needs to run 100% of the time to provide plant water, so delivery to the distribution system is controlled by a valve. When the tank reaches 'low', the valve at the plant opens and allows the tank to fill. When its full, the valve closes and the zone is fed by the tank. Similar setup as a standard pump on/off scenario but instead its a valve open/close.

The problem is, when the valve closes (and is no longer fed from the PS), the pressure drops from about 90 psi to 20 psi (or less) and takes about 30 seconds to recover to normal pressures (being totally tank fed). The tank is located pretty central in the zone and the pump station is at the southern end. The pressure drop is only seen in the area between the pump station and tank. All areas north of the tank are isolated from the phenomena and continue to get fed from the tank, as expected. The valve closes from 75% open to closed over a period of 2 minutes, so its not slamming shut, so transients do not seem to be the culprit.

Any idea whats causing this pressure drop and slow recovery? Why would the reservoir not simply take over and feed the area to the south? We have checked the check and altitude valves at the reservoir and all isolation valves on the line from the tank back to the plant and have ruled out issues there.

Attached are several events from our Telog pressure recorder, which samples at high frequency. The pattern appear like clockwork every time. Thanks for any feedback or ideas.

RE: Extremely unusual distribution system pressure drop

It would help if you could sketch this system as I can't work out if there is one pump station or many? or which pipes go where.

From what I can figure out from your text is the same pipe that you use to feed the water tank also used for distribution and is the pipe in question ( i.e. water flows in both directions in this pipe?)

what is the actuated valve arrangement and where are they in relation to your pumps and pressure sensor?

some sense of pipe size, flow rate, distance, tank size etc would help.

Some sort of interesting transient alright

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Extremely unusual distribution system pressure drop

(OP)
Attached is a sketch of the zone. Reservoir is one line in/out but located off of the mainline (flow can bypass it when filling).

Actuated valve is located on the plant site so its within a 1,000-ft of the pump station. Pump station is pressure controlled to maintain discharge pressure and valve is controlled by tank level. They are not interlocked as far as I know.

Pipe to the reservoir is a 12-in and flow to the reservoir from the pump station/control valve is less than 1,000 gpm. Reservoir is 0.5 MG. Distance from PS to reservoir is 5+ miles.

A thought that I had is possible air in the lines, but I really dont know. Don't want to go on that wild goose chase unless absolutely necessary. Thanks for any thoughts you might have.

RE: Extremely unusual distribution system pressure drop

3
Non cavitating water hammer, is my guess,
A more refined calculation is needed but
Speed of sound which is the speed of pressure (in water) is about 4000 ft/sec so it takes about 6.6 seconds for the wave to bounce from the tank to the valve. your peaks are at 8 seconds apart, this equals 6 miles, the 4000 ft/sec is for rigid pipe, softer pipes slow down the velocity a bit, so that lines up.

The 1000 gpm is a velocity of 2.8 ft/sec and going to zero is 2 minutes sounds fine but the flow only slows down when the valve is doing the very last turn or two, this is less time that the pressure wave has to communicate with the tank.

Rough numbers in water hammer, when the change in velocity is 1 ft/sec in rigid pipe there is a 50 psi change in pressure, when changing faster the the harmonic cycle, your bounces line up with this harmonic and the change in pressure lines up with a 1.2 ft/sec velocity change, so some of the slowdown has already happened or looping is lowering the velocity change

Solution, can you slow down the rate of closure of the valve? take 10 minutes on the full stroke, or if the controller is fancy, slow down the last 1/4 of the stroke, if the controller is very fancy have it do a pressure control on the down stream side of the valve when you want to stop filling, set it 10 psi lower than the normal pressure during that time and then set it to 10 psi higher that normal when you want to fill.
Question do you have a pressure spike during the start of the filling operation, or is the VFD a slow response

To refine the numbers, get a hydraulic surge analysis done. Some pressure tank manufacturers will do this for you for free, they will try to sell you a surge tank to solve the problem.

Hydrae

RE: Extremely unusual distribution system pressure drop

(OP)
hydrae,

Thanks very much for your desktop analysis! About 4 miles is a straight run and about 2 miles looped. Its ductile iron pipe, so your 6 mile estimation is spot on. I will definitely look closer at the valve closure speed.

To answer your question, there is no spike when filling either due to slow valve opening or slow response VFD or combination of the two. Thanks again!

RE: Extremely unusual distribution system pressure drop

I agree, this looks very much like a transient pressure wave issue.

If you could plot either flow through the valve and / or valve position you might see things a bit clearer.

I think you're just lucky that your flow is not enough to cause the water column to create a vacuum and hence the surge back could be very high.

Pipe systems of this sort of length are often the worst as it takes a reasonable time for the pressure wave to flow back and forth, but attenuation is limited.

What type of valve is your actuated valve?
how many times a day does it do this?
why can't you just continuously feed water into the system?

If you can fiddle around with the valve closure speed ( slower) or change it so that last bit closes slower like hydrae says. BTW that's a great reply by hydrae.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Extremely unusual distribution system pressure drop

(OP)
LittleInch,

As you can see from the sketch, the tank is not a flow through configuration, but is fill/drain, so we need to cut off supply to lower pressure and allow the tank to drain for water quality reasons. We could possibly find a scenario where we just throttle back the valve enough to drop pressure, but thats not the way its set up right now.

The control valve is a butterfly valve. It does about 1 to 2 cycles per day. Will definitely focus our efforts here. Thanks for your input as well!

RE: Extremely unusual distribution system pressure drop

No problem.

I see your double post got zapped - it's not good practice to double post here.

Also be sure and let us all know how you got on / what you found.

Butterfly valves are Ok at control, but not as good as proper control valves. You will still get a lot of flow through at quite a small percent open. Perhaps a smaller one would allow you to reduce flow to a more consistent flow to reduce the on / off nature of the valve.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Extremely unusual distribution system pressure drop

(OP)
I deleted the other post. Wasnt sure if this was the right forum for hydraulic questions. Guess it was! The butterfly is already reduced smaller than the line size to take that into account. Guess it still needs some tweaking. Thanks!

RE: Extremely unusual distribution system pressure drop

Fascinating!

I visited a company in Silicon Valley that made butterfly valves that were mechanically designed to be nearly linear clear down to shut-off. That could help with the "last little bit".

Keith Cress
kcress - http://www.flaminsystems.com

RE: Extremely unusual distribution system pressure drop

definitely a transient effect.

You have two flow scenarios which switch when you open/close the valve.

normal / tank drain: flow comes from the tank. It flows south and north feeding both ends of town.

tank fill: the plant provides water which flows north and serves the south end of town. Excess flow from the plant reaching the tank re-fills the tank and serves the north end of town. All flow moves north

opening and closing the valve causes the flow direction in the main transmission line to switch directions, with an associated temporary pressure fluctuation. Slowing down the valve will help.

RE: Extremely unusual distribution system pressure drop

Glad to help

Another thought, add a small bypass around the butterfly valve, say 2 inches with its own motor control valve. on a close command, close the big valve, upon contact with the limit switch, close the small valve (even better, make the small valve a pilot operated diaphragm control valve with solenoid control). Reverse the procedure for opening. This will give the system time to respond to the changes in flow.
You could program the system to leave the small valve open most of the time though this will slow down the freshness cycle on the tank. Caution, do not take a simple way by just adjusting the limit switch on the big valve so it never fully closes, this typically destroys resilient seated butterfly valves in just a few years.

Hydrae

RE: Extremely unusual distribution system pressure drop

In addition to the above comments, consider replacing the butterfly valve.

The butterfly valve has a very nonlinear, typically S-shaped flow curve. A butterfly valveā€™s flow characteristic is essentially closed until about 40 degrees, then flow increases from 20% to 90+% of capacity between 40 and 80 degrees. Butterfly valves offer quick opening and closing with a quarter turn. Such a narrow range of control and poor turndown makes butterfly valves a poor choice for control valve applications.

Consider replacing the butterfly valve with a linear operating globe valve.

http://www.singervalve.com/level-control-valves/10...

RE: Extremely unusual distribution system pressure drop

It would be really interesting to overlay your initial pressure graph with valve position / start / stop of closing.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Extremely unusual distribution system pressure drop

(OP)
LittleInch,

Our logger and SCADA clocks aren't synced so I cant get an exact overlay (they are a few minutes off), but I am assuming the vertical drop is where the valve goes to '0'. The falloff begins about 15 seconds before that at which point the valve is anywhere from 10% to 25% open (its not consistent).

RE: Extremely unusual distribution system pressure drop

As has been said, it is hard to close a ball valve slow enough, but closing slower will solve that problem. Taking a step further back, since you have a pump station that runs all the time anyway, and have to shut off flow to the tank to let it drain occasionally, the real problem is the elevated tank. Without the tank the pump station could just produce constant pressure all the time without any transients. The tower and fill valve that causes the transients will no longer be needed.

Water towers are really old technology. I find superior fire protection can be had for a fraction of the price by using generators to keep the pumps running and drawing from the main reservoir or aquifer.

RE: Extremely unusual distribution system pressure drop

the tower (albeit really old technology) is absolutely required for peak hour demands as well as fire protection. water storage in tanks is required for fire protection. and it would be unlikely that the 12 inch transmission main could provide adequate fireflow to the opposite end of town without the tank

RE: Extremely unusual distribution system pressure drop

Gravity works, even with the power out. There are many times the old tech is the best and water system operation is one of them.

RE: Extremely unusual distribution system pressure drop

Need to ask Los Alamos New Mexico how counting on a water tower for fire protection worked out. If your pumps are not big enough to handle peak demands and you don't have generators to keep those pumps running, you could end up in the same boat as Los Alamos and not have enough water to fight a fire.

RE: Extremely unusual distribution system pressure drop

I have no idea what you are talking about in New Mexico, however there is a good reason that municipal water systems have relied on storage reservoirs to meet both peak flow requirements as well as fire protection and emergency supply for 100's of years. Relying on pumps 100% of the time without backup and redundant systems is foolhardy.

RE: Extremely unusual distribution system pressure drop

Oh I believe in ground storage and generators! You could have a backup generator for the backup several times over for much less than a water tower cost. Then you have emergency water as long as you have fuel, not just until the tower is empty. I am sure Los Alamos now has generators and is no longer counting on a water tower to save their butts, because it was almost a catastrophe.

RE: Extremely unusual distribution system pressure drop

Quote (Valvecrazy (Mechanical))

If your pumps are not big enough to handle peak demands and you don't have generators to keep those pumps running, you could end up in the same boat as Los Alamos and not have enough water to fight a fire.

Not sure what you are referencing here. If you have an elevated water tower, the pumps are sized closer to the average daily demand to fill the tower, not the peak system demand.

RE: Extremely unusual distribution system pressure drop

The cities I work with are usually the smaller ones. I would never count on a single water tower to supply peak and/or fire flow demands. Ground storage with adequate booster pumps to supply max demands needed and backed up with a generator or two is the only sure way to have water in an emergency.

During a power outage a few years ago the city of Lubbock, where I live, which has several water towers was out of water in about 2 hours. And that was just a normal day with no emergency or fire. Now the city has at least one generator system to keep the pumps running, as they discovered water towers by themselves are not adequate.

RE: Extremely unusual distribution system pressure drop

Quote (Valvecrazy (Mechanical))

During a power outage a few years ago the city of Lubbock, where I live, which has several water towers was out of water in about 2 hours. And that was just a normal day with no emergency or fire. Now the city has at least one generator system to keep the pumps running, as they discovered water towers by themselves are not adequate.

Based on the news reports, the water outage had nothing to do with water towers. In fact, Lubbock would have been better served with water towers than ground storage tanks. It would appear that Lubbock lacked standby power or backup power for the water distribution pumps on the ground storage tanks. Every modern water distribution system should have backup power for water distribution pumps.

"The City of Lubbock has an extensive distribution system which includes 11 primary pump stations, 4 elevated towers and 13 ground tanks, and nearly 1,800 miles of underground pipes we call water mains - all designed to deliver water to our more than 83,000 service connections."

https://www.mylubbock.us/docs/default-source/water...

July 21, 2012

Lubbock, TX
Power Outage leads City Officials to issue boil water order. Loss of power crippled water distribution pumps, resulting in low pressure and potential for backflow of contamination or pollution into the drinking water supply

RE: Extremely unusual distribution system pressure drop

Quote (bimr)

It would appear that Lubbock lacked standby power or backup power for the water distribution pumps on the ground storage tanks. Every modern water distribution system should have backup power for water distribution pumps.

I believe that is exactly what I said. But I don't see how you could say the problems was not caused by the water towers lack of ability to handle an emergency? Afterwards Lubbock didn't add anymore towers, only generators.

My point is that even with multiple elevated towers, even a short power outage was enough to stop the water from flowing. Now with enough backup power, why are the towers even needed? Seems as in most cases the towers where just a false sense of security anyway.

Not to mention just how useless those towers are when there is a power outage for an extended period of time. Having enough generators with enough fuel is the only way to maintain the water supply when an ice storm or something keeps the power off for days or weeks at a time. For these reasons and many others I believe the 3000 year old technology of elevated towers is obsolete and a complete waste of taxpayer money.

But there is so much money spent purchasing and maintaining water towers that it is a completely political issue. I always get blasted just for mentioning it. Years ago after explaining this to a small city water manager, he looked at me and said, "boy don't you know there won't be any pressure without a water tower?" I tried to explain to him that the pump builds the pressure and supplies the water, not the water tower. But the "deer in the headlights" look he had meant he was never going to understand, which I am afraid is the case most of the time.

RE: Extremely unusual distribution system pressure drop

The selection of water storage facilities is not as simple as elevated versus ground storage.

There are a number of factors to consider when developing a water system including cost, population of municipality, topography, area of municipality, fire scenarios, water source, etc.

RE: Extremely unusual distribution system pressure drop

In this case, as in most of the cases I am tasked to help with, the water tower is the problem. The pump station runs all the time maintaining a constant pressure. The tower is not being used so the water quality becomes an issue. I know of many systems like this where at least once per day the pumps must be shut off or a valve to the tower closed, so the tower can drain and then be refilled with fresh water. As in this case, shutting off the pumps or closing the valve to the tower is causing the transients. Without the tower, the pump station would just maintain constant pressure to the system, the quality of the water in the tower would not be an issue, valves to the tower would not need to be opened or closed, and there would be no transients. Problem solved.

I am sure there could be backup pumps and generators for the backup pumps and generators several times over for much less than the cost of a tower, or even just maintaining the tower. As long as emergency water supply can be maintained in other ways, the tower would not be needed. Plus as stated earlier, these other ways to maintain emergency water supply can be much more effective than a tower when needed for long periods of time.

The calls I typically get are when the tower has a hole in it, needs to be inspected and painted, or the legs are too short to supply the pressure needed to distribution. I typically set the pump system up to maintain constant pressure, so the tower can be shut off for maintenance. During the month or three it takes to repair the tower I usually get a call from the water operator. He will say, "you know the pumps are not cycling at all so I am sure they will last longer this way". "The system pressure is so good the subdivision up on the hill has not called to complain about the pressure since the tower has been out of service." "We are no longer seeing transients or water hammer in the system, and line breaks have almost completely disappeared." "Not having line breaks also means we are wasting much less water in the distribution system." The conversation always ends up with the question, "So why are we spending so much time and money repairing the water tower"?

There are many better ways to supply water during a power outage. Plus towers cause so many problems with transients, valve speed, water quality, and other issues that my answer is always, "I don't know why you are spending so much repairing that tower".

RE: Extremely unusual distribution system pressure drop

(OP)
So we tried a scenario where we slowed the valve closure down to take about 8 minutes to close from 30% to closed and there was no transient. Pressure dipped slightly to about 55 psi before bouncing back to 65 psi when feeding from the tank. I say its successful! Thanks again for the tips!

Valvecrazy, I think you hijacked my thread ;) To speak to your proposed solution, most systems I work with benefit from having either ground storage or elevated storage (depending on topography), with an exception to standpipes, which tend to lead to more dead water. If you are sizing pump stations to handle peak hour and worst case fire flows, then you are over-sizing the pump station. "Textbook" design sizes pump stations for Max Day demand while tanks are used for peak hour, emergency and fire suppression and it has worked well in most all cases that I've looked at. It especially helps during peak hour for customers at the extreme ends of your system. If you are relying on pumps to push water to the end ends of your system and maintain adequate pressure, then you also have to oversize pipes or deal with pressure swings and major pressure fall off. Maybe small systems can get by without storage, but its a must for most any larger utility. If your customers are having issues with dead water or transients, then the design and operations need tweaking (like in our case) or the design was flawed (possibly bad tank sizing or placement). Now that this is behind us, we are back on track. No issues.

RE: Extremely unusual distribution system pressure drop

Wasn't hijacking anything, still on the same subject. Glad you were able to slow it down enough to reduce the transients. When you tell the doctor "it hurts when I do this", the doctor will say, "then don't do that". When you tell me closing a valve is causing transients and water hammer, I am going to say, "then don't close the valve". May not be what you want to hear as the tower would be useless. But when you have to make accommodations to regularly change the water in the tower for quality issues, then it sounds like the tower is useless anyway. You still have a transient causing a 10 PSI bounce even after taking 8 minutes to close the valve. You wouldn't see any of that if you didn't have to close the valve in the first place.

RE: Extremely unusual distribution system pressure drop

(OP)
Whats the largest water system, in MGD, that you have personally either designed or done an extensive hydraulic evaluation on that does not need elevated or ground storage?

RE: Extremely unusual distribution system pressure drop

I mostly work on systems that are 1MGD or less. But I see towers as even less useful in larger cities. For instance what good is 4M in elevated storage to a city like Lubbock that uses 38MGD? Just like last time, we will be out of water in a couple hours at best if they don't get some generators fired off. But people still think their water comes from those towers. LOL

BUT I never said ground storage was not important. That is where the REAL water comes from once they get the generators fired up.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close