Pressure inside the tank - Demineralize water tank

Pressure inside the tank - Demineralize water tank

Pressure inside the tank - Demineralize water tank

(OP)
Good morning guys,

I have demineralize water tank. According to the tank data sheet the tank need to be design based on 20 mBar pressure.

My question why we need to maintain that pressure inside the tank ?

Best regards,

Syah

RE: Pressure inside the tank - Demineralize water tank

Why- I can't help there.
But will point out that it is not uncommon for tanks to be specified with a design pressure higher than it needs to be- if it seems unreasonable, confirm with the person that wrote the data sheet that it is correct.

RE: Pressure inside the tank - Demineralize water tank

Is it gas blanketed?

Or is there some sort of vent with pressure?

A demin tank could be either.

20 mbar is a very low pressure so not a big issue.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Pressure inside the tank - Demineralize water tank

IMO, the water tank is open vent tank and the design pressure is for the venting of the roof deck limitation.

RE: Pressure inside the tank - Demineralize water tank

Demineralized water will absorb carbon dioxide from the atmosphere which will tend to increase the corrosivity of the demineralized water. Pure demineralized water without oxygen content is not corrosive.

Ultrapure water applications will add a nitrogen blanket to the air space of the demineralized water storage tank to prevent contact of the demineralized water with atmospheric air.

RE: Pressure inside the tank - Demineralize water tank

(OP)
Dear all,

Thanks for the respond.

These tanks have PVSV and anchor bolts as well. Each tank has 3 PSVS 12" size.

We will have pneumatic test at 1.25 x Design pressure on these tank.

BMR,

Do you mean if we just put goose neck vent like fire water tank, this demineralized water will absorp CO2 easily ?

Thanks and regards,

Syah

RE: Pressure inside the tank - Demineralize water tank

Syarhar,

I assume you mean you will add this pressure when the tank is completely full of water for the test. 25mbar (20 x 1.25) is equivalent to about 10" / 250mm of water only.

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.

RE: Pressure inside the tank - Demineralize water tank

(OP)
Little inch,

Yes that is what we are going to do.

We will follow API 650 appendix F.7.5.

Syah

RE: Pressure inside the tank - Demineralize water tank

Quote (Syahar1975 (Mechanical))

Do you mean if we just put goose neck vent like fire water tank, this demineralized water will absorp CO2 easily ?

Correct. Demineralized water has a good affinity to absorb carbon dioxide and oxygen from the atmosphere, and both lead to metal surfaces corrosion.

https://books.google.com/books?id=JUyFdLxlJ1YC&...

This may or may not be a problem for your application, but is a common problem for high purity water.

RE: Pressure inside the tank - Demineralize water tank

You can add a CO2 scrubber if you want to prevent carbonic acid accumulation.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close