Trip coil supervision relay 7PG17

Status
Not open for further replies.

jose78

Electrical
Joined
Feb 6, 2018
Messages
4
Location
OM
Hi frinds,

I like to know why reset time is more than 400ms in TCS relay(7PG17). Please clarify.
 
how much do you need it to be? what problem has it caused?
 
I don't know about the 7PG17 relay, but in general you need a time delay while other relays may be tripping, as the Trip coil monitor relays would be blind during this time.
 
This is what I found in the relay catalog:
Quote "These relays incorporate a time delay on de-energisation to keep the relay in an operated condition during temporary reductions in the battery voltage." Unquote.
I guess the 400ms is to provide time for DC supply changeover etc. (without giving rise to unnecessary alarm in the mean time) and is a beneficial feature.
You haven't mentioned what is the difficulty is is posing in your system. It makes learning two way.