Exi vs Exd transmitters in oil/gas industry

Exi vs Exd transmitters in oil/gas industry

Exi vs Exd transmitters in oil/gas industry

(OP)
Hi

I have following question. Why do we often use Exi pressure, level or temperature transmitter in II zone (methane) with appropriate Intrinsic Safety isolators whereas total cost of combination Exi transmitter with Intrinsic Safety isolators mounted in control cabinet is more expensive than Exd transmitter mounted in the field alone?

Thanks in advance for answers!

RE: Exi vs Exd transmitters in oil/gas industry

Good Question, why would you use Intrinsic Safe, I work in related industry but we seldom do any more. It's not just the hardware but to do it right special cable, dedicated trays, segregated panels.

Occasionally you strike a situation where Intrinsic Safe is the only approval you can get for a particular instrument. I'm looking at a guided wave radar in a tank with Hydrogen gas. I dare say the barriers will be somewhere close by.

I don't see Exi in the Methods of Protection list Ex ia, EX ib, Ex ic
There are so many variations in hazardous location designation, can you share the location of the project, complete hazardous zone designation?

RE: Exi vs Exd transmitters in oil/gas industry

One point to pay attention is the whole cost of the implementation.

You can't only consider the prices of the equipment; you need to analyze the whole project. Usually, you need considerable structure, and you spend more time to implement an Ex d than an Ex i project.

The cost per hour of people involved in the installation and project + the cost of devices should be the right analyze before say that Ex i is more expensive than Ex d in all projects.

One example is the Wireless projects, where the cost of devices are higher than standard devices but you save money in time and installation cost.

I'd like to read an opinion from colleagues with more experience with this type of projects.

Thanks

RE: Exi vs Exd transmitters in oil/gas industry

Ex'd' hardware is expensive but the supporting infrastructure is simple and conventional. No special earths, no exotic overload relays, no awkward design, no limitation to low-powered instrument circuits. I'd contend that an Ex'd' installation may work out cheaper in some instances. Equally in Zone 0 then Ex'ia' is the only option open to you, so there isn't even a choice to be made.

It depends on the overall installation. There is no single answer which is universally accurate. The design engineer should be looking for the lowest cost solution which meets the technical requirements of the specification.

RE: Exi vs Exd transmitters in oil/gas industry

As mentioned above, some applications come only in Ex-i due to the medium.
Ex-d installations will end up more expensive than Ex-i if Junction Boxes and local control stations are also bought Ex-d. And the hassle of maintenance to Ex-d boxes..
A good designer would use Ex-d instruments but place the JB's outside hazardous Zone 1, use Ex-e JB's for an optimum solution. But this is not so obvious to EPCM companies these days..

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close