INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?
2

Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

(OP)
I have a question regarding the concrete cover requirements for a slab in ground.

Does having a plastic vapor barrier (6 mil to 10 mil) change the 3" cover requirement for concrete 'cast against & permanently in contact with ground?'

Could the cover requirements be reduced? Personally, I don't think it is a great idea to reduce them, but I wanted to get other opinions.

Below is the ACI table...

Thank for input!

RE: Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

If just a slab on ground, it would not be structural, so I don’t think the ACI code would apply.

RE: Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

A vapor barrier is just that, and is not a water-tight seal (as typically installed and used). I don't think that using one would change the ACI classification of being in contact with earth.
Dave

Thaidavid

RE: Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

(OP)
Hokie- you are correct. ACI 318 section 1.4.7 specifically says that 318 does not apply to slabs in ground.

But.....I think that 318 might still apply. Here is my argument...

I should state that I am talking about cover for conventional or post-tensioned ribbed slabs where you get 24"-36" beams and 4"-6" thick pad areas.

As mentioned, ACI 318 does not apply to slabs in ground. So, I went to ACI 360, which covers Slabs on Ground.

To the best of my knowledge, ACI 360 does not provide any guidance on concrete cover. Also, if you have a slab supporting building code loads, then ACI 360 refers you back to ACI 318. See below excerpt from ACI 360.

My reading is that If we follow ACI 360, then I think we should apply the ACI 318 cover provisions.

I'm confused and open to input?





RE: Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

For ribbed foundation slabs, I would treat them as footings, so the cover provisions would apply. A vapor barrier would not change the requirement, but a membrane would.

RE: Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

Rebar should be approx 2" from the top of the slab, so, 3" cover to soil shouldn't even be an issue.

Dik

RE: Reinforcement Concrete Cover for Slab in Ground - Plastic Vapor Barrier?

IMO no, I believe the common 3" requirement deals with the variations in the subsurface elevation and stability during a pour. I say keep it at 3".

Depending on the size of the job. We have found it beneficial to pour a mud slab using lean concrete to form a stable level base to build off of. In this case 2" of cover would be acceptable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close