×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Contact US

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

SOG Turndown for Tenant Slab

SOG Turndown for Tenant Slab

SOG Turndown for Tenant Slab

(OP)
Hey everyone,

I'm working on a steel framed retail/office building where the interior slab on grade will be the tenant's responsibility. We will still need to provide the wall footings and a band of slab for the light gauge infill walls to attach to. My plan was to show a typical slab turndown onto the wall footing and maybe a 1'-2' wide band of interior slab around the perimeter. The alternative would be to provide a stem wall to support the light gauge. The stem wall is much less concrete but would require additional formwork. The turndown seems like the easiest option but I wanted to be sure I'm not overlooking any ill-affects. Any of you have hesitations using my approach?

Thanks in advance.

RE: SOG Turndown for Tenant Slab

If the interior slab on grade will be placed by the tenant at a later date, just do the stem wall.
It leaves an empty space for them to route any plumbing or electrical along the exterior and avoid the need for dowels or a visible construction joint.

RE: SOG Turndown for Tenant Slab

When i design a turned down slab, I typically rely on the counterweight of a portion of the interior slab to resolve the eccentric loading. If you only have a strip, you would have not have a fat enough guy on the end of your teeter totter. It still can work - just gotta check the numbers.

RE: SOG Turndown for Tenant Slab

(OP)
Thanks for the insight. I'm leaning toward the turndown with a strip of slab about 3'-4' wide to help with eccentric loading XR250 points out. The architect is fine using this and we should still have plenty off room where the plumbing needs to go.

RE: SOG Turndown for Tenant Slab

Here's a photo of a turn-down slab method on a project from some time ago - steel framed commercial.

The owner had all sorts of problems with the joint between the first exterior slab strip and the subsequent tenant-provided interior slab.
Essentially the interior slab moved relative to the exterior slab (or visa-versa) and the joint opened up and created problems with floor tile, bumps in carpet, etc.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: SOG Turndown for Tenant Slab

JAE's point is well taken. If the tenant is to provide the slab on ground, leave it to him. Make the external structure independent.

RE: SOG Turndown for Tenant Slab

A little off topic, but I'm curious - is this a common arrangement, having the tenant responsible for the slab? Seems like a very bizzare setup, having everything included but the floor.

RE: SOG Turndown for Tenant Slab

It likely 50/50 around here for that arrangement in CRUs. It allows each tenant to run their required mechanical sub-slab while allowing the developer to "finish" the building.

RE: SOG Turndown for Tenant Slab

@JAE:

Was that due to slab curling?

RE: SOG Turndown for Tenant Slab

No - we believe it was mostly settlement in the exterior footing (within allowable ranges) but with any downward movement the piece of slab extending into the building a few feet acts like a wing and the entire gradebeam & "wing" section then rotates with the wing end coming up relative to the interior slab.

They also most likely didn't provide any dowels or other means of resisting vertical differential movements across the joint.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: SOG Turndown for Tenant Slab

(OP)
CANPRO - I have not had much experience with this arrangement but for projects involving developers it seems relatively common for the reasons that jayrod12 mentions.

JAE - if properly keyed joints and dowels are used I wouldn't think that the result in your figure would be an issue. Although I feel a little less certain now ha!

RE: SOG Turndown for Tenant Slab

A stemwall removes the possibility of that sort of rotation outright. That would be the way I would go. It can't be much more expensive and then it is done "right".

RE: SOG Turndown for Tenant Slab

Around here, the developer usually pours the whole slab and they cut it up as needed. It is super efficient :>

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close