Fiber Optic Cable Service Loop

Fiber Optic Cable Service Loop

Fiber Optic Cable Service Loop

(OP)
Is there a Code Requirement to leave service loops for Fiber Optic Cable? I have heard and read lengths of anywhere from 10' to 100' but I do not see anything in the NEC that explicitly says that a service loop of any length is required. Does anyone know of one?

RE: Fiber Optic Cable Service Loop

I couldn't find an answer to your question, but I did come across this section of the NEC that might interest you.

770.48 Unlisted Cables Entering Buildings.
(A) Conductive and Nonconductive Cables. Unlisted conduc‐
tive and nonconductive outside plant optical fiber cables shall
be permitted to be installed in building spaces, other than
risers, ducts used for environmental air, plenums used for envi‐
ronmental air, and other spaces used for environmental air,
where the length of the cable within the building, measured
from its point of entrance, does not exceed 15 m (50 ft) and
the cable enters the building from the outside and is termina‐
ted in an enclosure.
 The point of entrance shall be permitted to be extended
from the penetration of the external wall or floor slab by
continuously enclosing the entrance optical fiber cables in
rigid metal conduit (RMC) or intermediate metal conduit
(IMC) to the point of emergence.

RE: Fiber Optic Cable Service Loop

The NEC code would be more aligned with safety that maintainability. Look up BICSI standards regarding fiber. Service loops are always recommended. Its easier to perform one mid-span splice using a service loop than creating two splices, fitting a piece of cable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close