We have a rosemount 5302 guided wave radar and configuration and and variables are all setup but we have a setback our fouth variable is signal quality. We get our variable but we are trying to scale it from 0% to 100% and send the value to our HMI. Does anyone know the ranges of the signal quality? I realize this is something very minor but any help would be appreciated. P.S. the Emmerson sight was totally and unhelpful at all dont recommend using it for questions.
RE: Rosemount 5300 series
http://www.emerson.com/catalog/en-us/rosemount-530...
In the Manual it says:
The Signal Quality spans from 0 to 10, where 0 indicates a low margin, and 10 indicates a
high margin. It indicates how much margin there is until the noise peak is indicated as the
surface level.