Cascade controller set-point units

Cascade controller set-point units

Cascade controller set-point units

(OP)
When a controller accepts a remote set-point in cascade mode from another (primary) controller does the output of the primary controller have to be scaled into the engineering units of the secondary measured value (MV)?

RE: Cascade controller set-point units

Yes.

xnuke
"Live and act within the limit of your knowledge and keep expanding it to the limit of your life." Ayn Rand, Atlas Shrugged.
Please see FAQ731-376: Eng-Tips.com Forum Policies for tips on how to make the best use of Eng-Tips.

RE: Cascade controller set-point units

As Xnuke says: Yes.

But, I've worked on some DCS Systems that don't allow changing the Output Engineering Units of the Primary Controller - they were always 0 - 100% and could not be changed to match the engineering units of the secondary controller (like degC). It's very frustrating.....

______________________________________________________________________________
This is normally the space where people post something insightful.

RE: Cascade controller set-point units

input the controller output signal into a math block, scale it, use the math block output

RE: Cascade controller set-point units

(OP)
Thanks controlnovice. On the DCS systems that don't support changing of engineering units is it just assumed that 0 to 100% output of the primary controller represents 0 to 100% of the the secondary controller measured variable? I.e. if the secondary controller measured variable is 0 to 50 litres/min then the remote setpoint is also a 0 to 50 litres/min signal?

RE: Cascade controller set-point units

Yes:

0-100% of the Master controller output represents the full range of the Secondary controller PV...in your example 0 - 50 lpm.

Keep in mind that typically the Setpoint range of the secondary controller matches the PV Range...so your SP Range would also be 0 - 50 lpm.

If you limit your setpoint maximum to, for example 40 lpm, the 100% output still represents the 50 lpm but the secondary controller won't go above 40.

______________________________________________________________________________
This is normally the space where people post something insightful.

RE: Cascade controller set-point units

(OP)
Thank you this was really helpful.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close