Waste Water Screening Room - NFPA -820 - ventilation/pressurization

Waste Water Screening Room - NFPA -820 - ventilation/pressurization

Waste Water Screening Room - NFPA -820 - ventilation/pressurization

(OP)
I am looking at a screening room for waste water. NFPA-820 calls for <12 air changes per hour. As a math nerd, that reads to me as less-than 12 ACH, but I think it is supposed to be greater-than. It is a Class 1 Division 1 area. So I am supposed to have at least 12 air changes per hour in the room.

The NFPA-20 also says that this room needs to be -0.1"WC relative to ambient. That is a substantial negative to maintain in addition to a 12 ACH ventilation rate. The room is roughly 18,000 cubic feet, so 12 ACH is roughly 3,600 CFM. But now how can a -0.1" WC be achieved on top of that? The exhaust will need to be substantially higher than the supply.

In a truly sealed environment this could probably be easily calculated. It could also be done with some idea of the envelop cracks. In the case of this room, however, there is a channel of water under the "floor", which is steel grating. the channel comes from a combination storm/sanitary sewer, and goes to an underground holding tank that is surely vented. How can any kind of negative be pulled in a building with the gaping openings of a channel running underneath it?

I don't see how both criteria of 12 ACH and -0.1"WC can be achieved. Anyone ever run into something like this?

RE: Waste Water Screening Room - NFPA -820 - ventilation/pressurization

Since you are a math nerd you should be able to derive the air flow requirements based on the allowable concentration of whatever hazardous or toxic vapor is generated. It is a simple procedure of air in, air flow out containing the allowable concentration of the toxic vapor or fume, and the generated toxic or hazardous vapor from the waste water. The equation will be a first order D.E. having an exponential (decay) function for a solution to determining the exhaust CFM. The American Conference of Industrial Hygienist (ACGIH) or NIOSH which is OSHA enforceable regulation publish these allowable concentration for 8 hour work exposure. Normally, the allowable concentrations publish by ACGIH or NIOSH will be similar.
Another aspect that you should be aware is that the room volume that will be require in the D.E. does not necessarily mean the entire room since the air flow could be stratified and consequently the room volume could be taken within the breathing zone so for safe keeping up to 10ft. high if there is no elevated work zone.

RE: Waste Water Screening Room - NFPA -820 - ventilation/pressurization

Most of these screening rooms are Class I, Div. 2. Ask the electrican to compare the cost of Div. 1 to Div. 2.

The latest edition of NPFA states "Continuously ventilated at 12 air changes per hour" for Class I, Div. 2 applications such as you are decribing. Class 1 Division 1 is no ventilation or ventilated at less than 12 air changes per hour.

The -0.1"WC is a measure of how tight (in terms of building air leakage) the building is. You can't meet this standard with building doors open.

http://c.ymcdn.com/sites/www.ncsafewater.org/resou...

Regarding: "How can any kind of negative be pulled in a building with the gaping openings of a channel running underneath it?"

Come on man, be a little creative. You can furnish a water seal where the water must flow under a baffle wall to seal.

Some applications supply sealing covers over the channels.

Regarding: "Another aspect that you should be aware is that the room volume that will be require in the D.E. does not necessarily mean the entire room since the air flow could be stratified and consequently the room volume could be taken within the breathing zone so for safe keeping up to 10ft. high if there is no elevated work zone."

This is an incorrect statement and not included in NFPA 820.

RE: Waste Water Screening Room - NFPA -820 - ventilation/pressurization

"This is an incorrect statement and not included in NFPA 820" My advice has nothing to do with the NFPA 820 and it is an acceptable method described in various ventilation literature such as "Ventilation for the Control of the Work Environment" authored by William A Burgess, Michael J Ellenbecker and Robert D Treitman. NFPA's approach is undoubtedly conservative and even perhaps wasteful in electrical consumption and capital investment, nonetheless, the OP has options to select.

RE: Waste Water Screening Room - NFPA -820 - ventilation/pressurization

Another source of information that would be valuable come from articles written by certified industrial hygienist Jeff Burton who has written numerous article on industrial ventilation and his articles have been predominantly published in the periodical titled Occupational, Health and Safety. His approach is similar to the one I originally described and if you can do research on his work, you will have a different view point from NFPA. If you do use NFPA guideline, remember the volume to be exhausted does not necessarily mean the entire room as you can partition the points of origin of the contaminants or even duct the exhaust with hoods.

RE: Waste Water Screening Room - NFPA -820 - ventilation/pressurization

bimr hit the nail on the head. Class 1 Div 1 (Zone 1) electrical equipment is an order of magnitude more costly than Class 1 Div 2 (Zone 2) equipment. The economics of producing a Div 2 environment, by means of mechanical ventilation is usually easy to justify in most industrial situations.
GG

"I have not failed. I've just found 10,000 ways that won't work." Thomas Alva Edison (1847-1931)

RE: Waste Water Screening Room - NFPA -820 - ventilation/pressurization

As with any modification to an existing facility, your design will be influenced by the areas outside your scope. Start with the MAU based upon the 12 x/hr. based upon gross room volume (no allowance for equipment). Class/division rating will affect the MAU election and power/controls. I have used indirect gas fired b4 with TEFC motors w/o issues. Locate MAU and control panel outside the class/division area. Utilize a remote sensor in the proper enclosure. You may be forced into steam or exp. proof electric duct heater as the heating source. Place the equipment outside the room to keep power & control wiring costs down. Dynamic FDs at walls. Second, estimate the free area of the open piping / trench connected to the ÔÇťother space(s). I estimate 800-1200 fpm and the resulting CFM of the connected area should give you the DP you are looking for. I have used this in production areas when 2 spaces must be controlled to a dp between rooms. Utilize a VFD with a DP integrated control loop. Install VFD and controls outside Class/Div room to avoid wiring issues. Greenheck has GB fans with exp. resistant construction. If cannot pass with a GB fan, utilize an in-line with motor out of air with bronze and aluminum. I would look at dp between rooms and not dp to atmosphere. Your reference leg may be very negative to start.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close