rising floor...

rising floor...

rising floor...

(OP)
I looked at a house built in 2007, where there appears to be a growing hump in the first floor. Floor joists (TJIs) run parallel with a CMU wall that has a little wood stem wall above it and is in place of a TJI at that spacing location. The wall below doesn't line up with the wall above, of course. The TJIs are level - they don't appear to be deflecting much at all, according to my 4' level - but there is a definite upward hump over the length of the stemwall/CMU location. There is no obvious movment of the wall, or cracking in the CMU, or swelling in the stemwall, that could be seen from below in the unfinished basement space. We don't have swelling soils around here.

Anyone have any idea what's going on with this?

Please remember: we're not all guys!

RE: rising floor...

Obvious hard point/line in the floor system relative to the floor joists.

Can you post a plan of the floor framing system with the miss aligned stacked walls showing too?

Mike McCann, PE, SE (WA)


RE: rising floor...

(OP)
You asked for it - my AMAZING drafting skills, in action. TJIs are 16" deep and 16" oc. Wall is 8" unreinforced CMU, not retaining. This is one of those crazy McMansion-type houses that was built when the county didn't have time to inspect every house during construction, so there's flat no telling what's happened.

Please remember: we're not all guys!

RE: rising floor...

Is the rise roughly consistent along the span of the TJIs? If so, I would suspect that the bearing walls have settled, but the NLB CMU wall hasn't. Thus the "rise" in the floor system at that point.

RE: rising floor...

(OP)
The rise appears to be greater near the middle of the span of the parallel wall. There is no indication of differential settlement between the CMU wall shown and the exterior bearing walls (no cracking, etc).

Please remember: we're not all guys!

RE: rising floor...

You have a relative stiffness issue with the hard bearing line of the CMU wall below compared to the stiffness of the parallel joists, and you are reading the deflection of the floor joists at midspan. That is the reason that it seems like the center of the CMU bearing wall is lifting. It is all relative.

Mike McCann, PE, SE (WA)


RE: rising floor...

Span of the TJIs?

Have you set up a laser level and checked the bottom chord of the TJIs for deflection. Not noticeable to the naked eye on the bottom is still enough for a noticeable hump in the floor above.

RE: rising floor...

(OP)
That's what I figured - just wanted to make sure I wasn't missing something big.

Now - what do I tell them to do about it? I'm considering stiffening the floor trusses, perhaps jacking them with a beam.

Please remember: we're not all guys!

RE: rising floor...

(OP)
jayrod12 - didn't yet. I checked with my level, but I think by the deflection pattern that you're exactly right.

Please remember: we're not all guys!

RE: rising floor...

Does the wall provide lateral support? Is the wall above load bearing?

If the answer to both of those questions is no, then I would look at providing supplementary wood members on either side of it, and removing the cmu wall.

If either of those answers is yes, then there aren't really any feasible options. It's a poor design layout.

RE: rising floor...

(OP)
Removing the wall isn't really feasible, because one side is unfinished but concrete floor for storage but the other has just raw soil cut away at this wall. I agree - totally a poor design.

Cheers, folks, and thanks for the help.

Please remember: we're not all guys!

RE: rising floor...

Or you could replace the CMU wall with a beam under the wall above of the same EI and overall deflection characteristics as the floor joists...

Or, if the floor joists can tolerate it, add a transverse beam supporting the TJI's at midspan, framing to the CMU wall footing and whatever beyond.

Mike McCann, PE, SE (WA)


RE: rising floor...

Complete removal isn't necessarily required, just enough removal that the wall no longer supports the floor. Take out the top course. It could still act as a demising wall.

This is all of course subject to seismic and stability detailing depending on the location.

RE: rising floor...

Quote (SLTA)

a CMU wall that has a little wood stem wall above it and is in place of a TJI at that spacing location

Seems that the CMU wall below has a small stem wall on top of it, that is now load-bearing.

Can the "little stem wall above" the CMU wall be removed to temporarily (permanently?) 'de-load' the floor system at this location and be rid of the 'bumb'?

RE: rising floor...

(OP)
Ingenuity - it could be removed, except that it's also in place of one of the TJIs at that spacing location. I think I'm going to have to tell them to deal with it.

Please remember: we're not all guys!

RE: rising floor...

Does the deck/sheathing cantilever to support the wall above? If yes, could the CMU wall below flat and level while the wall above is causing the sheathing to deflect creating the hump?

RE: rising floor...

Not likely at all. That would be very non-standard framing.

Mike McCann, PE, SE (WA)


Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close