Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

(OP)
We have multiple feeders from a piece of SWGR to multiple SWBDs. These feeders are 1600A’s each so we are running parallel feeders using a separately run #4/0 AWG Ground. The Contractor wrote an RFI in order to try a save the owner money and requested that we run a single ground cable for the multiple feeders and tap off the single ground into the SWBDs instead of running individual grounds back to the SWGR. His justification was that it met Article 250.122 (c). My initial thought was that this is something that can save money and seems to make sense in doing as such. I believe that further down in that article in 250.122 (f) for parallel feeders it points to article 310.10(h) and stipulates that the parallel feeder (phase, neutral, and ground) must adhere to 310.10 (h) (2) which says it must have the same length, consist of the same material, be the same size, have the same insulation, and be terminated in the same manner. This reads to me that the contractor’s suggestion is not allowed because the same length and circular mill, and being terminated in the same manner would not be satisfied.

Am I reading the code properly or is this not it’s intent?

RE: Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

Are these "parallel" feeders in multiple conduits? If so, you must run a separate full sized ground wire in each conduit. I'm not sure what you mean by "separately run" ground wire, but the ground wire must be in the same conduit as the phase conductors to be an effective ground return path. I'm too lazy to research the NEC for you, but if you're running these feeders in conduit, I'm pretty sure it requires each conduit to have its own equipment grounding conductor. Regardless of what the Code says, however, it is good engineering practice to put a ground wire in each conduit when there are multiple conduits in a feeder.

RE: Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

Interesting.
I find myself "building per print", and questioning things less and less as the years pass, but I can say that only very, very rarely (if ever) do I recall having dealt with equipment grounding conductors of the same circular mils, length, etc., as the phase conductors in parallel feeders. These installations are all inspected by people whose lives revolve around the "NEC". I'm too lazy also to go digging through my books and references right now, but 310.10(h)(2) is certainly applicable in very specific instances only. I'm curious about what you found out and how your own application was resolved.

.


Me wrong? I'm just fine-tuning my sarcasm!

RE: Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

(OP)
>>>HCBFlash (Electrical)20 Nov 16 18:41
>>>Interesting.
>>>I find myself "building per print", and questioning things less and less as the years pass, but I can say that only very, very rarely (if ever) do I >>>recall having dealt with equipment grounding conductors of the same circular mils, length, etc., as the phase conductors in parallel feeders. These >>>installations are all inspected by people whose lives revolve around the "NEC". I'm too lazy also to go digging through my books and references right >>>now, but 310.10(h)(2) is certainly applicable in very specific instances only. I'm curious about what you found out and how your >>>own application was resolved.

Everytime you have to run feeders above the ampacity of a single conductor cable you run into this situation which in my industrial line of work is very often. I have never been asked by a contractor to splice the grounding conductors on major feeders but on the surface it seems to be something that could be a cost savings approach as long as the NEC allowed it. The direction I gave was for the contractor to route vertical trays into the switchboard instead of conduit as to allow the single EGC in the tray versus having to run the EGC in each of the set of conductors in order to satisfy the NEC 310.10(h)(2).

Thanks dpc and HCBFlash for taking the time in providing me your thoughts on the matter!

RE: Parallel feeders and is corresponding Ground conductors 250.122 (c) and (f) and 310.10 (H)

Just to clarify, by "full-sized" ground conductor, I mean each ground conductor in each conduit must be sized per applicable NEC table (Article 250) as it was the only ground wire. I did not mean to imply that the ground wire had to be equal in size to the phase conductors. It may be, but it is sized per Article 250 for the total circuit rating.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close