bookowski
Structural
- Aug 29, 2010
- 983
I have a condition where my elevators do not have any columns immediately adjacent, i.e. they fall somewhere within a bay (steel framed building). The machine rooms are in a bulkhead that extends 22ft above the roof. See rough sketch attached showing the typical framing and posts for the bulkhead above. the machine roof framing is carrying by 4 posts which land on the typical framing.
My questions/concerns are:
- Looking at static loads and L/1666 deflection limitation, how far do I carry this and how do I apply it. Should I do all beams in the load path until the column as L/1666? That clearly doesn't guarantee any overall deflection limit
- Is there any overall deflection limit?
- Is the main concern a differential movement related to machine operation or is there also some component that is concerned with overall elevator movement that would be felt by the occupant (i.e. if all my beams collectively deflect 1" even though each is L/1666)
- At 22' the bulkhead has some wind on it, do I apply an l/1666 criteria for those supporting beams in combo with static elevator loads?
The columns were omitted here due to some existing conditions and the inability to place footings in the area.
The beams are huge to satisfy what I think is a safe interpretation of the above - I'm wondering if I'm being overly conservative.
I've also considered adding corner columns for 1 or 2 stories only to assist in deflection.
My questions/concerns are:
- Looking at static loads and L/1666 deflection limitation, how far do I carry this and how do I apply it. Should I do all beams in the load path until the column as L/1666? That clearly doesn't guarantee any overall deflection limit
- Is there any overall deflection limit?
- Is the main concern a differential movement related to machine operation or is there also some component that is concerned with overall elevator movement that would be felt by the occupant (i.e. if all my beams collectively deflect 1" even though each is L/1666)
- At 22' the bulkhead has some wind on it, do I apply an l/1666 criteria for those supporting beams in combo with static elevator loads?
The columns were omitted here due to some existing conditions and the inability to place footings in the area.
The beams are huge to satisfy what I think is a safe interpretation of the above - I'm wondering if I'm being overly conservative.
I've also considered adding corner columns for 1 or 2 stories only to assist in deflection.