Isolated footing near wall
(OP)
I have to design a footing in an existing building for a new steel column which is located right next to an existing exterior CMU wall footing. In other words, the column would be sitting on the edge of the footing. I would appreciate tips on how to go about it (Shear considerations, etc.) ACI Code. I am only considering gravity loads as it is a low seismic area.
RE: Isolated footing near wall
Jason McKee
proud R&D Manager of
Cross Section Analysis & Design
Software for the structural design of cross sections
Moment Curvature Analysis
Interaction Diagrams
Reifnorcement Design etc.
RE: Isolated footing near wall
2. Abut new footing to existing strip footing using drilled dowels into existing concrete. Strap new footing to another interior footing if necessary and if practical.
BA
RE: Isolated footing near wall
It usually takes quite a bit of footing self weight to make edge loaded footings work without employing some kind of strap/rectifying beam.