Endress Prowirl F200 Steam Flow Meter

Endress Prowirl F200 Steam Flow Meter

Endress Prowirl F200 Steam Flow Meter

(OP)
Greeting,
We have installed Prowirl F200 DN80 on Saturated Steam, against following operating condition which was given by client.

Flow: 8000lbs/h , Pressure: 10 bar , Temperature: 170C, Line Size 6 inch

Applicator display the following outputs for these conditions
Meter Size: DN80
Velocity 41 m/s
Pressure Loss: 75mbar

After installation transmitter display measuring value as following.
Mass Flow 7193.13 kg/h ;;; is it mean the instrument size suitable for flow of 3628Kg/h but big meter size required for 7193.13 kg/h
Velocity 94.15 m/s
Temperature 173.49C

Client have query about pressure loss and claim the instrument drop the pressure 2 bar boiler running on 9 bar and production area receiving the 7 bar pressure after instrument installation.
Could you share your views about this problem.
Replies continue below

Recommended for you

RE: Endress Prowirl F200 Steam Flow Meter

What kind of answer are you fishing for?

You posted on the CR4 forum (link below) and neglected to reveal that the meter was sized for 8000lbs/hr, where as the process flow is in excess of 7,200Kg/hr. That's where the pressure drop comes from - excessive flow rate.

Link

What's to say about it?

It's sized wrong.

RE: Endress Prowirl F200 Steam Flow Meter

(OP)
Dear danw2, thanks for reply, we are not fishing actually we have selected flow meter against attached provided operating conditions.
http://files.engineering.com/getfile.aspx?folder=b...

and not neglected to reveal on CR4 as stated mentioned there "is it mean the instrument size smaller then flow of 3628Kg/h big meter size required for 7193.13 kg/h"

There is no other instrument installed on this line and having no body idea about exact figure of flow that's why they claim us your meter is measured wrong value which is 7193kg/h our production department needs only 4000kg/h may be they loss extra energy anywhere,
furthermore there is installed 13t/h capacity boiler which is connected on this line.

So how can we prove to client that your actual flow is 7113kg/h which is measuring on transmitter display and they provided us 8000lb/h for meter selection.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close