Balcony Collapse in Berkley, CA
Balcony Collapse in Berkley, CA
(OP)
See link:
http://www.latimes.com/local/lanow/la-me-berkeley-...
http://www.latimes.com/local/lanow/la-me-berkeley-...
"We shape our buildings, thereafter they shape us." -WSC
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Key word, normally, I've also heard more than one engineer argue that since they are off of a 40psf design load suite that the balconies can be designed for 40psf. I don't do that, but I know some who do.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
These wood cantilever balconies scare the crap out of me for this reason. All developers want to do them, but there is no redundancy and a failure is sudden.
To avoid water infiltration issues, we typically just cantilever 2 PT beams, one at each end. No repetitive for redundancy.
And that would be a 60 psf live load per code. Not 100. You could argue 40.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
Speaking as a non-botanist or biologist, but as a 6 year forestry student, all rot is fungal in one way or another. All rot needs water to become established, some les some more, but dry rot after it is established will proper and continue to grow and spread and degrade the wood with just a little moisture in the air or frequent applications of environmental moisture.
Jim
p.s. Those broken wood ends looked wetter than dry rot but may have been dry rot anyway. Hard to tell with out close examination. the lawyers will have a field day and well they should.
RE: Balcony Collapse in Berkley, CA
So sad for their families.
RE: Balcony Collapse in Berkley, CA
Shouldn't have failed if it was designed for 40psf. Wood has an average safety factor of 2.5.
Bouncing up and down would be like an impact loading. Wood is 2x stronger for impact loads. They'd have to bounce up and down with the same frequency as the floor joists to get some resonance.
Regardless, what a shame. Someone f'd up and 6 people had to pay the price with their lives.
RE: Balcony Collapse in Berkley, CA
Why would PT joists and decking not be specified?
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
joist breaks appears irregular and discolored (dark, not fresh wood)
loading 2007 required the balcony to hold at least 60 pounds per square foot
4'x6' = 24 square feet
24 x 60 = 1140 pound design capacity
13 people on balcony = ???
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
But there's probably thousands of balconies that are designed the exact same way.
Very sad. People send their kids to the US to get more education and this happens.
RE: Balcony Collapse in Berkley, CA
Maine Professional and Structural Engineer. www.fepc.us
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
The moisture barrier on top of the deck could have failed quite a while ago, allowing water intrusion over an extended period of time. This deck probably gets a lot of sun and rain as well, which sets up a wetting and drying cycle. There has probably not been much if any waterproofing maintenance which allowed the wood deterioration to advance to the point that the joists had only a fraction of their original capacity.
The building owner should inspect all other decks, particularly on this face of the building and initiate immediate structural and waterproofing repairs.
RE: Balcony Collapse in Berkley, CA
Must have saved hundreds of dollars. I wonder if it was worth it?
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
Grace Bitumen pan failed. 40 mil PVC pan might have performed better.
RE: Balcony Collapse in Berkley, CA
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
http://www.nytimes.com/2015/06/17/us/balcony-colla...
'Muricans collapse balconies all the time, and no such tone. Perhaps the 1800's and NINA are still with us.
RE: Balcony Collapse in Berkley, CA
http://www.sfgate.com/bayarea/article/Berkeley-bal...
I hope there are no decorative bridges or overpasses.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Seems increasingly plainly a water issue...
The "decorative" concept is inconceivable to me. I've seen 'decorative balconies' in hotels with less than 12" cantilever and absolutely inaccessible by persons. But a double door with a 4' balcony absolutely invites the party outside. I assume everyone will crowd onto a balcony and lean over the rail to watch the sirens go by....
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
The photo posted above does suggest lack of a proper drainage system. Rainwater was likely allowed to pond on the surface of the balcony, spreading over its surface. I think this is why we see fairly uniform deterioration of all of the joists; if there was localized deterioration, then I would have blamed a leaking drainage system.
To compound the situation, I question whether there was a proper moisture barrier in place that would have prevented - or at least limited - the amount of water infiltration into the joists.
Furthermore, one (or two) of you suggested that the header directly below should also be investigated for possible deterioration due to water infiltration. I agree that this possibility cannot be ruled out. This brings to light something about this type of problem that is so often overlooked: we need to open pandora's box, so to speak, and question the current state of all the other balconies in this structure. After all, the intent of the building code is life safety!
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
It could be something as simple as someone nailing on a top surface to the decking and puncturing the rather flimsy plastic sheeting that is evident.
Not building at least the main spars out of steel is simply a recipe for disaster. will be interesting if we ever see what the balcony under looks like once they've stripped off the deck.
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
We build plenty of outdoor decks out of wood. I don't see many steel ones.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
That being said, what do you think would be an appropriate code modification?
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
All balconies or porches 4 feet or more above grade require all structural framing and connections to be moisture resistant (i.e. pressure treated wood and stainless or galvanized metal) and detailed to prevent moisture related failure (proper drainage).
Maine Professional and Structural Engineer. www.fepc.us
RE: Balcony Collapse in Berkley, CA
"Annual inspections are so important for all balconies and terraces, but particularly for ones made of wood," he said. "In fact, rotting wood is the biggest cause of balcony and terrace failures."
Are annual inspections required by the building code?
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
I don't know of any required annual inspections, I understood what he said as essentially "annual inspections are a good practice, especially for wood balconies".
Maine Professional and Structural Engineer. www.fepc.us
RE: Balcony Collapse in Berkley, CA
Regardless, as a good practice these should always be PT, even if covered to avoid failures like this. Even if they are PT wood, my concern is what happens in 20 years when the PT is essentially gone and the wood needs to be replaced?
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
Didn't know PT wore out. Is that true?
RE: Balcony Collapse in Berkley, CA
" the life span of properly treated posts should be at least 20 years"
A residential deck has about a 20 year life span. Longer if not exposed, but a wet piece of wood (or steel) won't last 50 years.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
For a platform suspended high above the ground there clearly should be a back-up support to prevent collapse in the event of failure of the main support.
Specifying adjusted load factors, or more stringent durability control is not the answer. It needs a different approach.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Balcony Collapse in Berkley, CA
And even more appropriate, methinks.
RE: Balcony Collapse in Berkley, CA
The material technical resource sheet is publication TJ-1020 from Weyerhauser.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Why can't ACI come out with an "Appendix D" for decks?
RE: Balcony Collapse in Berkley, CA
TABLE R502.3.3(2) CANTILEVER SPANS FOR FLOOR JOISTS SUPPORTING EXTERIOR BALCONYa, b, e, f
Member Size Spacing Maximum Cantilever Span
(Uplift Force at Backspan Support in lb)c, d
Ground Snow Load
≤ 30 psf 50 psf 70 psf
2 × 8 12″ 42″ (139) 39″ (156) 34″ (165)
2 × 8 16″ 36″ (151) 34″ (171) 29″ (180)
2 × 10 12″ 61″ (164) 57″ (189) 49″ (201)
2 × 10 16″ 53″ (180) 49″ (208) 42″ (220)
2 × 10 24″ 43″ (212) 40″ (241) 34″ (255)
2 × 12 16″ 72″ (228) 67″ (260) 57″ (268)
2 × 12 24″ 58″ (279) 54″ (319) 47″ (330)
For SI: 1 inch = 25.4 mm, 1 pound per square foot = 0.0479 kPa.
a. Spans are based on No. 2 Grade lumber of Douglas fir-larch, hem-fir, southern pine and spruce-pine-fir for repetitive (three or more) members.
b.[u] Ratio of backspan to cantilever span shall be at least 2:1.[/u]
c. Connections capable of resisting the indicated uplift force shall be provided at the backspan support.
d. Uplift force is for a backspan to cantilever span ratio of 2:1. Tabulated uplift values are permitted to be reduced by multiplying by a factor equal to 2 divided by the actual backspan ratio provided (2/backspan ratio).
e. A full-depth rim joist shall be provided at the unsupported end of the cantilever joists. Solid blocking shall be provided at the supported end.
f. Linear interpolation shall be permitted for ground snow loads other than shown.
Top Previous Section Ne
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
There are some screen shots of drawing details here as well.
http://www.berkeleyside.com/2015/06/19/no-smoking-...
RE: Balcony Collapse in Berkley, CA
Do you think anyone would attempt to design a wood cantilever balcony connecting into a face mounted plate?
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Why doesn't the membrane extend up and into the dwelling instead of being used to funnel water into the wood? There's no other drain path provided.
RE: Balcony Collapse in Berkley, CA
But I am suspecting the ripped to slope joists or maybe the deck topping, something resulting in ponding.
RE: Balcony Collapse in Berkley, CA
Childress Engineering Services structural engineer Kevin Liu reviewed the designs and photos, and said the structural design of the wood beams and joists met building codes then in effect. He said the deck's two major cantilever beams -- 1 3/4-inch by 11 7/8-inch each, at each side of the balcony -- appeared to fail, "and then the rest of the joists and beams went down with it."
RE: Balcony Collapse in Berkley, CA
Further, it appears that there was a water intrusion line about a foot off the joist attachment. This indicates a linear breach of the membrane. Was the first joint or the counterflashing joint not adequately sealed? Only a proper investigation will determine.
Even though we're not there and can only speculate, it is clear that the balcony waterproofing design and construction were contributing factors.
RE: Balcony Collapse in Berkley, CA
The rot seems to be maximum where the detail indicates the flashing would end. The lower balcony had some leakage but did not look rotted. Maybe the lower balcony had the flashing over the membrane; the membrane extended up the wall; the caulking was better for some reason; the upper balcony deflected the majority of water from that part of the lower balcony.
RE: Balcony Collapse in Berkley, CA
Requirements: Insightful, engineering analysis, 1200 words, minimum, 2 pictures, minimum. Need by: ASAP
Please reply back if you are available and interested. Any summary or thoughts on what you would like to develop in the article beyond what is suggested above would be appreciated. Also, do estimate how soon you could submit this article. With news stories, time is of the essence and we are already a little late with this one.
Roopinder Tara
Director of Content
ENGINEERING.com
rtara@engineering.com
RE: Balcony Collapse in Berkley, CA
Well, that opinion makes me want to pull my hair out. Though, thank God their job title wasn't listed as building "engineer". We don't need more fuel to fan this fire: http://www.eng-tips.com/viewthread.cfm?qid=180126
I look forward to reading the op-ed. Could you provide a link in this thread when it has been posted, RoopinderTara?
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
It would be irresponsible for any of us here to write the article you want. We can all speculate, and some things are obvious, but any detailed analysis of this collapse will have to be done by the investigators in Berkeley. In case one or more of our members are involved in the investigation, I think they will not be releasing a report any time soon.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Someone mentioned the white deposits on the wood remnants. That is most likely salts coming out of the wood AND fungus byproducts, it is very commonly seen on wood that has been routinely or repeatedly wet.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Any wood structure exposed to the elements that is used as a deck, balcony,walkway,or any related purpose shall be constructed of pressure treated wood elements. If enclosed construction it is to be vented by an area of 1/180 s.f.of structure. Vents shall be removable for periodic inspections.
RE: Balcony Collapse in Berkley, CA
If a building code modification is in order then I had something in mind that is actually a combination of hokie66 and manstrom's ideas. Maybe something to the effect of:
b) Employ hatches, ports or similar devices in the concealing finishes to allow future inspections of structural members and connections.
c) Be designed for 200% of the loads set forth in ASCE 7-XX.
However, I don't believe that code modifications are an effective way to address this issue. At the end of the day the people footing the bill for this collapse will be insurance. There would most likely be more real-world impact if insurance companies required inspections, offered rate discounts for inspections, or at the very least included some very specific smoking-gun questions in their application/questionnaire and seriously hike the rates depending on the answers. Changes won't happen until there is the threat of someone's wallet getting lighter...
RE: Balcony Collapse in Berkley, CA
At a previous employer, I investigated an entire school that was constructed such that the wall cavity held standing water, and in his wisdom, the architect had permitted (in writing) the builder to leave off the waterproofing on the exterior face of the wallboard behind the brick. It was so bad that the steel stud exterior framing was completed rusted through in many places. The entire exterior of the classrooms was removed - brick, stud wall, insulation - and replaced between the last day of spring semester and the first day of fall semester.
I am watching a cheap wood apartment complex going up near my house. (The structure is cheap, not the rent, based on what I see locally.) Not 20 minutes ago, I drove by and observed the balconies in various states of completion. 2x6 or 2x8 framing, a rim joist against the lap siding and/or EIFS, enclosed underneath with solid boards of reconstituted wood. Having watched the job go up from the recently cleared earth, including the spunbound polyolefin moisture barrier go on, I would lay odd that they will have water problems in short order. A lack of diligence in waterproofing is a pet peeve of mine. Shoddy construction costs us all a great deal.
(Now, if they had constructed it of reinforced concrete...
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Can you upload a clearer version of that structural plan?
RE: Balcony Collapse in Berkley, CA
About 20 years ago I had to recommend that all the cantilevered wood balconies on a 6 year old low rental housing be cut off due to rot found on some of them. I was a very unpopular person at the tenants's meeting called to explain the recommendation. However the recommendation was followed and they had no more balconies. Thank goodness.
RE: Balcony Collapse in Berkley, CA
I'd be much more comfortable requiring stainless steel connectors and a higher preservative treatment. There are ones that last a lot longer than 20 years. Per AWPA U1 (Link), decks have a use category of 3B or 4A. They should increase it to 4C or even marine.
Per home depots website, pressure treated lumber has a chemical retention of 0.05 lb/ft3 using MCA. This seems low.
If you look at Table 15-5 in the wood handbook (Link), you can see that there are plenty of treatment options that will last longer than 20 years. Increasing the retention in most of the treatments resulted in NO failures after a substantial amount of time.
I'd rather have a certain level of preservative treatment and stainless connectors in conjunction with the inspections every so often.
RE: Balcony Collapse in Berkley, CA
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Balcony Collapse in Berkley, CA
http://www.berkeleyside.com/2015/06/19/no-smoking-...
Regarding the backspan of the balcony beams and joists, 2:1 is best practice but not code required. The failure wasn't in the backspan lifting up, the beams and joists sheared off.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
"
Based on their observations, city staff recommended that the Berkeley City Council adopt new and modified regulations to enhance the safety of all current and future buildings in Berkeley.
The recommended changes would make new balconies and other sealed areas that are exposed to weather subject to stricter requirements on materials, inspection and ventilation. The proposed rules would also require regular maintenance inspections for all such spaces for future and existing buildings.
"I'm going to propose, similar to San Francisco, owners get a structural engineer to inspect the buildings every five years," Eric Angstadt, director of Berkeley's Planning and Development Department, said at a press conference Tuesday.
"
RE: Balcony Collapse in Berkley, CA
If the balcony was indeed 4ftx6ft as stated somewhere above and the code in force at the time of construction required 60psf design live load, then the balcony was in fact overloaded at the time of the failure if there were 13 people on it as reported in some of the articles linked above, since 4x6x60/13 = 110lbs per person and people weigh more than 110 lbs.
It is interesting to note that the 2012 IBC, currently in effect in many locations, has reduced the balcony live load to "same as occupancy served", which for multifamily buildings like this one, is 40psf for private rooms. The 2006 IBC required 100 psf for balconies serving private rooms of multifamily buildings like this one and allowed the use of 60psf for balconies serving 1 and 2 family dwellings if the balcony was less than 100sf. This reduction from 100psf to 40 psf was quite significant and unconservative in my opinion, and I will not be surprised to see it revert back to 100psf in future editions of IBC. Does anyone know what is required by 2015 IBC on this?
Nevertheless, from the photo posted above, it seems rather obvious that the cantilevered joists were pretty deteriorated from rot caused by water infiltrating into the building envelope and that rot was a significant contributing factor to the collapse of the balcony.
Several of the comments calling for requiring regular inspections seem well intentioned and sound good politically, but a meaningful inspection of this type of construction would be impossible since the framing is all concealed within the building envelope.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Quote (Hammurabi)
If a builder build a house for some one, and does not construct it properly, and the house which he built fall in and kill its owner, then that builder shall be put to death."
Not really, since it's often more than just a single factor that causes these things; a lazy, or malevolent, owner is not exactly a rare thing.
As for inspections, that's just going to be another tax that will jack up the cost of living. I'm forced to do a backflow valve test every year, which is $25, so not that bad, but a structural exam is going to cost $200?
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
We'd be left with diligent, nice owners.
Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies
RE: Balcony Collapse in Berkley, CA
1. Periodic inspections would not solve a hidden problem like this. They would just create, as Irstuff said, another tax.
2. Failures rarely occur due to overloading, they occur due to defects. So changing code live loading will have little effect.
3. The statement above that the flashing should have been turned out above the topping slab is wrong. The topping slab is for protection of the membrane, not to serve as such.
RE: Balcony Collapse in Berkley, CA
(Despite the somewhat unclear plans photo, I will weight in on what seems to be a problem so designers will avoid it.)
That drawing seems to show a saw cut top chord of the cantilever lumber. This would probably change the grading of the lumber and if pressure treated, would remove the treated wood and open it up to moisture intrusion. It also opens up endgrain right at the area where the flashing most likely leaks at the face of wall.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Exactly!! I wish architects and contractor could understand this!!
RE: Balcony Collapse in Berkley, CA
Sure, but there're also be a lot of innocent, but dead, builders.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
I wish they would as well, but we continue to get these incorrect comments from engineers, who should know better.
RE: Balcony Collapse in Berkley, CA
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
The balcony loading did not change in the 2015 IBC. The code is online at http://codes.iccsafe.org/I-Codes.html
ASCE 7--10 lists balcony live load as 1.5 times the load for the area served, not required to exceed 100 psf.
RE: Balcony Collapse in Berkley, CA
You don't think the difference between 40psf and 100psf is significant?
RE: Balcony Collapse in Berkley, CA
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
The next shows the moisture barrier under the metal flashing, protecting the potentially exposed portion of the barrier. The barrier is continuous and water is prevented from contacting the wood, while being able to be absorbed and evaporated through the concrete.
Some details are omitted from both images - the filler board, the caulk, and the door details.
RE: Balcony Collapse in Berkley, CA
Thanks for the heads up on the 2015 IBC loading. I have the ASCE 7-10 back at the office but I didn't cross check it vs the 2012 IBC, which is what is currently in effect in my state, so it's what I typically default to. It's interesting to note the difference between IBC and ASCE 7, thanks for pointing that out. Personally, I think I will default to 100psf for cantilevered balconies in the future, which is what I was used to from the 2006 IBC before my state's last code cycle.
In the case of this particular Berkley balcony the design live load may well have been a mute point because of the wood rot resulted from inadequate waterproofing, but in general the difference between 40psf and 100 psf is massively significant, and even in the case of this Berkley balcony, in the hands of a good lawyer (I am not a lawyer, not even a bad one), if the design live load was in fact exceeded, that could be end of story.
RE: Balcony Collapse in Berkley, CA
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
There is a big difference in 40 PSF and 100 PSF, but in all the building failures I know of or have studied, details and defects have caused them, not overloading.
RE: Balcony Collapse in Berkley, CA
ASCE 7-10 says 1.5 times occupancy use. 100 psf max. (60 psf for residential)
ASCE 7-05 say 60psf for 1 and 2 family residences, 100 psf for public.
IBC 2009, 2012 and 2015 say same as occupancy served. (40 psf here)
In 2006 IBC, it was 60 psf for 1 and 2 family, 100 psf for public.
Regardless of loading, what is the capacity of a rotten 2x10?
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
Good summary of design live loads from recent common codes and referenced standards. You have further illustrated precisely the wide variation of design criteria commonly used in practice that I pointed out in my initial post above. Regarding your rhetorical question about the capacity of a rotten 2x10, I don't disagree with your point.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
I wish. Developers are loving the look. Wood buildings now don't look like wood buildings. They want them to look like concrete or steel with big cantilevers. Hopefully this instance will help to talk them out of it.
When I am working on a problem, I never think about beauty but when I have finished, if the solution is not beautiful, I know it is wrong.
-R. Buckminster Fuller
RE: Balcony Collapse in Berkley, CA
I agree with you that 40/60/100psf design load would only affect when a failure like this might tragically occur. In light of the apparent waterproofing defects in this case, from the perspective of Architecture/Engineering/Construction industry principles and practices, the design live load requirement may indeed be immaterial to a failure analysis of this case. From a logic point of view though, and a perhaps a legal one (I am not a lawyer), the design live load may not be immaterial. For example, answer the question, if a healthy balcony would be permitted to fail under 41psf or 61psf, then why should an identical rotten balcony be required to support 62psf or 102psf or more?
I disagree that the key takeaway for us should be to avoid cantilever spans for wood balconies. There is no fundamental reason why cantilevered wood balconies are any more susceptible to this type of failure than balconies constructed from steel or concrete. I have personally witnessed steel framed balconies with over 50% loss of cross section from corrosion resulted from improper water proofing. Like the wood joists in this Berkley case, the steel framing was completely enclosed by architectural finishes and there was no way to detect the problem visually. That is, until the balconies began to deflect a couple of inches and the rim joist, which in this case was a rolled steel channel, disintegrated to the point that you could easily take a look inside the floor cavity through the fist sized holes!
RE: Balcony Collapse in Berkley, CA
I agree - that is the symptom. The problem is that owners/developers want extremely low $/sqft construction costs and then compound that condition further with a lack of maintenance and inspection. When the starting $/sqft value is low, then it undergoes one or more rounds of V.E. a quality waterproofing contractor and/or quality materials aren't affordable. If owners/developers were hit with a giant insurance premium for pursuing cheap construction it mitigate that problem some...
I was an expert witness in an analogous suit a few years ago where the owner/developer (same person) successfully showed that they were oblivious to the fact that severe V.E. cuts compromised the overall integrity and quality of the finished building. The architect's insurance ended up footing the bill because, "the architect should have better communicated to the owner that reducing construction costs so severely would result in a sub-standard quality building".
John Klein, P.E., M.L.S.E.
www.johnkleinpe.com
RE: Balcony Collapse in Berkley, CA
That is a very instructive outcome in the case you describe.
RE: Balcony Collapse in Berkley, CA
@gte447f
By the way, if I'm correctly assuming the origin of your username I was gte312d once upon a time.
John Klein, P.E., M.L.S.E.
www.johnkleinpe.com
RE: Balcony Collapse in Berkley, CA
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
I invite your comments, observations and additions.
Roopinder Tara
Director of Content
ENGINEERING.com
RE: Balcony Collapse in Berkley, CA
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
One is that the slope of this balcony would increase as the supporting wood rotted.
Two is that the natural frequency of this balcony would decrease as the supporting wood rotted.
Three is to set an allowable deflection change for an applied load; up to setting a pool on the balcony and filling it to match the allowable load.
The problem for the first two methods is that it requires keeping records of how the item performed initially. The ideal would be that there is no change, but there would be some measurement error and some mass change as the wood and concrete moisture content changed, which would affect the results.
The initial problem for the third is that one needs to keep a record of what the expected deflection is. The next problem is that time and possibly heavy equipment is required. The biggest problem for the third is that the structure might fail during the test and do a lot of damage; people could be safely removed from the area prior to the test, but it might make a simple repair much more complicated. I can imagine a cascade of balcony failures as the top one and its load dropped onto the next and repeated down the side of a building.
Of the methods I like the natural frequency check the best. The change in frequency would be very dramatic for a change in the section properties and not as dramatic for smaller changes like moisture content. Slope change is difficult to measure as the item may not be uniform, making a good comparison a problem. The most certain method is to load the item to the design limit, assuming there is some factor of safety, but it has a high expense and when an item fails the test, has a lot of unwanted side-effects.
RE: Balcony Collapse in Berkley, CA
Also, one of the updates says that there was "dry rot". Wood rots only when exposed to moisture and microbes, so I suggest your technically-oriented website stick to proper terminology.
RE: Balcony Collapse in Berkley, CA
In regards to the article, I would have to say it is a commentary based not only on this forum but also draws upon the author's experience, which is considerable and quite relevant to the subject.
I would encourage you, and others, to share your views of this and other subjects outside this forum. I know as an engineer, I take comfort in talking to other engineers and this forum is great for that, but ENGINEERING.com offers a way to get reach a bigger audience, one that can benefit from learning from professionals in active practice. So much of what we read is supplied but non-technical and non-expert authors. Most engineers would like to read on engineering subjects outside their discipline, for example. Also, with any big news story, the public needs to be informed. If there is an engineering angle, such as this balcony disaster, who better to write the article than an actual structural engineer? Sure, we have to be careful we don't speculate but most of us in the engineering professions are not prone to that.
I'm still looking for someone to write more on this subject, as we have not yet covered the maximum load the balcony may have had, compared to what it could be designed for (40/60/100 psf?) And what about dead vs live load? As it has been pointed out, humans crowded on to a balcony is beyond normal for the rest of the dwelling. The pieces of this article are here in the forum but would anyone care to work on an article with me?
best,
Roopinder Tara
Director of Content
ENGINEERING.com
RE: Balcony Collapse in Berkley, CA
My reason for replying is simply to correct what may be a possible error as presented by the article posted above. The article mentions that the construction type is an "outrigger" balcony and not a "cantilevered" joist balcony. The difference being that the cantilevered beams on each end are the only structural support versus all of the joists being cantilevered supports. It appears to me (although it is hard to tell from the photos) that this is actually a "cantilevered" joist balcony. Can anybody confirm this?
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
BA
RE: Balcony Collapse in Berkley, CA
However, I have no intent upon interfering with the investigation. As stated in the article, I give all due respect to the ongoing forensic investigation and I certainly do not intend to interfere with that effort. It is not my intention here to suggest that the failure had anything to do with the chosen method of framing. I think we are all clear on that point and we are looking at cause related to the flashing resulting in deterioration of the wood framing.
The article was presented as an opportunity to learn something from this experience - focusing upon a certain characteristic that will likely be "brushed aside" as not relevant to the investigation.
I also wish to express gratitude to all who have contributed to this thread.
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
While there was some speculation that this balcony shielded the one below, which exhibited, as near as I can tell from photos, almost no rotting, rain water would still have gotten onto the lower balconies. This possibly suggests that the actual construction on that one particular balcony was deficient, which aggravated the less than ideal design. I had that sort of thing happen in my new house; we got some water intrusion, and it turned out that the tar paper had gotten damaged and torn in ONE spot, and water managed to get down to the hole and entered into the wall.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Found the pic I was referring to. This pic is what led me to think that this is an outrigger system. If anyone has more information on the type of framing system employed (a pic of the structural drawings showing the framing system would be ideal), please feel free to post it on this thread.
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
Leave it open for inspection so it's not "Out of sight - out of mind."
RE: Balcony Collapse in Berkley, CA
I agree with BS2 that the joists appear to be cantilevered. What leads me to that conclusion is the photo of the failed joists. They all failed at the exact same location along the span as the two edge cantilevered members that are larger in cross section (i.e. the two you refer to as outriggers). In the system you refer to as an outrigger system, I assume that you are implying that only the two edge members are cantilevered, and that the infill joists are simply supported spans between a ledger at the exterior face of the building and an edge beam spanning between and perpendicular to the two cantilevered outriggers at their free ends. If what I have described is an accurate description of what you refer to as an outrigger system, then I don't think that the infill joists would fail in the manner that we see in the photo. Don't you think they would fail at the simple support at the ledger at the face of the building?, especially if it was a toe nailed connection, which it would have had to be since we don't see any joist hangers at the face of the building. I don't think this is the system that we see in the photo. They clearly look like cantilevered joists to me.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
Yes, the stubs remaining of these joists have not significantly rotated as a result of the failure, and that does suggests some measure of restraint to keep them somewhat horizontal; however, there was not much strength left in these members to cause such a rotation at the moment of failure.
We have a lack of information, gentlemen, and we are jumping to conclusions. Again, all I have to go on - as shown on the pic I have posted above - is that the outlying "joists" are thicker than the other joists. This leads me to the likelihood (not certainty of course) that these are outriggers. Why else would these members be thicker than the others?
So, yes, of course I may be incorrect in stating that this is an outrigger system. But the point of my article was NOT to insist on this, rather, to suggest an opportunity to explore two types of balcony construction.
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
So, yes, that is a true cantilever system rather than an outrigger system. I was fooled by the larger members in the pictures. The joists were "ripped" to allow the shallower depth required for the concrete deck on the balcony.
Anyways, although I have stated in the article that this is an outrigger system, the intent of the article does not hinge upon what this particular system actually is.
Richard L. Flower, P. E., LEED Green Associate
Senior Structural Engineer
Complere Engineering Group, Inc.
RE: Balcony Collapse in Berkley, CA
The 2nd is the type that collapsed which consist of cantilevered from an inset inside the floor edge lam beams and between them non p.t. joist.The blocking at the interface of the building makes it hard to see the inset joist.
My theory is that the stucco leaked into the wall from an area about 16' high and with no deck above to block the rain dripped into the wall behind the flashing and floor membrane.Also flashing nails are highly suspect.
I see no weep screed at the base of floor 5 to drain water.
Also the membrane looked short and not going up behind the metal flashing on the detail at the door.It also looks like the decay occurred at the membrane lap.
I'll have info from the man at the scene.
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
1) The balcony was designed and built from non pressure treated wood as a cantilever design with no significant level of redundancy
2) It was highly unlikely that it was designed to hold 13 people in a 6 x 4 space even at new condition, but no notices existed to that extent
3) The failure of ALL the beams at seeming the same location close to the building indicates a failure of the water proofing, the details of which are seen in posts above
4) Confining the wooden supports within a structure which did not allow either inspection or drainage of any water entering the envelope is poor design
5) Placing a 2 1/2" concrete screed above the beams is not a good idea
6) Similar structures are recommended to be either removed or inspected to show adequate strength of the beams on a regular (1/2 year) basis, especially for those locations where there is no rain cover above them
7) Load limits should be noted / posted on similar balconies
8) More info to come from the scene in due course
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
RE: Balcony Collapse in Berkley, CA
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
BA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
I am retracting my previous statement. I am not fond of the engineering.com article, particularly because of the ratio of (potential social good/potential personal gain) I get from reading it.
The Balcony Collapse in Berkeley, California: What Can We Learn from This?
What *was* a layperson supposed to learn from the article? How to be informed/persuaded by conjecture and vagueness?
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
Do you mean points 1-8 or point 9.
I agree that it is premature to decide the exact cause of collapse of the balcony, but it certainly isn't premature to discuss how similar events can be prevented. The fact that we don't know what happened here, or what might happen in the future under similar situations, is the exact reason why structures must be designed with sufficient redundancy to prevent total collapse when the unexpected happens.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
Redundancy is great, but this balcony had redundancy. Closely spaced joists provide redundancy...until they all fail.
RE: Balcony Collapse in Berkley, CA
Clearly it did not have enough redundancy.
Multiple members supporting a cantilever subject to a more or less uniform load does not provide redundancy.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
The article mentions the building code but fails to provide details on what sections are applicable to this balcony. I'd love to see an article that points out the various code requirements that are there to prevent this failure (or show the lack of such requirements if that's the case). Plus, with the correction that this is a cantilever system the entire section regarding cantilever vs outrigger is not relevant and quite biased. Reading the article you would think that an outrigger system should never be used. But this impression is suddenly opposed in the conclusion which basically seeks to counter all the claims of the first three parts of the article (but the header for this conclusion is "wood not always appropriate" so I'm not sure what the conclusion actually is).
Where are the facts?!
There's also two lines I'm having a lot of issue with:
"I merely wish to point out that the failure of one outrigger beam would cause collapse of the entire balcony whereas failure of one cantilevered joist would not necessarily cause collapse of the entire balcony."
This is 100% conjecture. A very strong outrigger balcony, even with only two outrigger beams, could possibly suffer the loss of an outrigger though unintended paths of support and not collapse. Conversely, a cantilever system could just as easily fail after the loss of a single member if the remaining members were already heavily stressed. Yes, I gather the point was that cantilever systems are typically more redundant than outrigger systems but this sentence does a great job of showing the problems of conjecture and confirmation bias that are found throughout the article.
"Indeed, the structural engineering community should have had the foresight to address this issue before lives had been lost."
No. Just no. This is very much the authors personal opinion AND grossly inaccurate in my opinion (and hopefully to many others). We have no idea what the structural engineer on this project did or did not do unless someone runs the numbers on the design. The balcony could have been well over-designed and still failed due to rot and that's not the engineers fault (unless they also were in charge of the moisture protection). In addition, we don't know if it was the architect, contractor, or owner that caused or exacerbated the moisture damage and failure. Regardless, the structural engineering community had no practical way to prevent this (again in my opinion). Does the article imply that I should go look at the balcony of my apartment, my neighbors apartment, and anyone else who has a balcony in my local area? Does the article imply that no balcony can survive without regular inspections? Obviously as a licensed engineer if I am aware of a unsafe condition then I ethically must address it but how was the engineering community supposed to prevent this failure?
Yes, the engineering community should always strive to identify areas where the building codes do not provide a sufficient minimal level of protection but the article doesn't even address whether the code was sufficient or not.
As MacGruber put it, the article is full of "conjecture and vagueness".
rlflower, I'm being very, very harsh here I know. This isn't personal but I'm also trying to be fair here. This is a high-profile failure and I feel that to not be 100% critical about the things we engineers state publicly would be poor service to the engineering community. We need to be sure our statements publicly are based on facts and well thought conclusions (which is also required by our ethical obligations).
- Engineers shall issue public statements only in an objective and truthful manner.
- Engineers shall be objective and truthful in professional reports, statements, or testimony. They shall include all relevant and pertinent information in such reports, statements, or testimony, which should bear the date indicating when it was current.
- Engineers may express publicly technical opinions that are founded upon knowledge of the facts and competence in the subject matter.
- Engineers shall issue no statements, criticisms, or arguments on technical matters that are inspired or paid for by interested parties, unless they have prefaced their comments by explicitly identifying the interested parties on whose behalf they are speaking, and by revealing the existence of any interest the engineers may have in the matters.
Maine Professional and Structural Engineer. www.fepc.usRE: Balcony Collapse in Berkley, CA
In my opinion the author of the article violated the engineering ethical requirement that "engineers shall be objective and truthful in professional reports, statements, or testimony. They shall include all relevant and pertinent information in such reports, statements, or testimony, which should bear the date indicating when it was current" and that "engineers may express publicly technical opinions that are founded upon knowledge of the facts and competence in the subject matter."
I don't consider it to be egregious enough to warrant it but I also would not think it improper for this to be brought to an engineering board.
Maine Professional and Structural Engineer. www.fepc.us
RE: Balcony Collapse in Berkley, CA
My earlier comment applies to items 1) through 8) for reasons I do not particularly wish to discuss at this time, but it applies also to item 9).
I am trying in vain to think of an example of a structure where collapse could NOT lead to human death.
Are you sure you want to make a code provision requiring sufficient redundancy so that a structure does not collapse when any element fails? Where is the redundancy in a simple beam carrying floor or roof members if the simple beam fails or if one of its end connections fails?
BA
RE: Balcony Collapse in Berkley, CA
So, clearly all structures must now have a height restriction of 4 feet or be designed with 100% redundancy.
Maine Professional and Structural Engineer. www.fepc.us
RE: Balcony Collapse in Berkley, CA
I think that already existed. If any single cantilever had failed, the balcony could probably have survived that. ALL the cantilevers failed, and it was overloaded.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
It collapsed because there was no effective redundancy.
As has been discussed already, there are several mechanisms by which cantilevers might be constructed so that they don't collapse if the primary support fails, but this balcony did not have any of them, in common with many other balconies in the world.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Maine Professional and Structural Engineer. www.fepc.us
RE: Balcony Collapse in Berkley, CA
You can't prevent all deterioration of materials. Structures should not collapse when their materials deteriorate, especially when collapse results in people falling to their death.
By redundant I mean that it should have sufficient strength in some other load path that it doesn't collapse. There are many different ways of doing that, including using materials that will have large deflections before they lose strength.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
Thaidavid
RE: Balcony Collapse in Berkley, CA
The statement: "Any structure where collapse could lead to human deaths must be designed with sufficient redundancy so that it does not collapse when any element fails." is supposed to be a statement of a general principle, not a design standard clause.
Certainly it's easy to interpret in such a way that it doesn't make sense, but it is also possible to interpret it in context, in a way that does make sense. The question is, if we do that, does it imply that the design of some structures should be handled differently? I think it does. The questions below relate to all accessible external balconies anywhere in domestic or public buildings:
- What is the maximum load that can be expected over the life of the structure? - As many adults as can squeeze onto it.
- What is the probability of significant deterioration of the supporting materials over the life of the structure? - In many cases high.
- What is the probability that this deterioration will go undetected or untreated? - In many cases high.
- In the event of one supporting member failing what would be the result? - In many cases sudden total collapse, likely to result in multiple deaths.
- Are there any practicable measures that could be taken to significantly reduce the probability of such an event? - Yes, there are several.
So other than a very small increase in the overall construction cost, what is the drawback to a requirement that balconies should be designed to be safer in the event of overloading and/or deterioration?
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
The fact that in this particular case a report does not mention lack of redundancy as a factor just shows that the standard approach to design for collapse needs to be changed.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Connecting the parapet rail to the wall is the third way that has been mentioned.
I don't see anything wrong with any of those options.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
I don't know how you could expect that to practically and predictably work.
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
Another easier option is use steel floor joist or angle irons.
Or a 2 way slab on junior I beams.
If you look at the photo of the railing it is very heavy duty.
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
The building seems to have an extensive exterior stairway leading down the face of one end of the building. Hmmm, I wonder if it should be checked as it looks to probably have the same sort of drainage needs as the ill fated balcony.
Google Satellite
Keith Cress
kcress - http://www.flaminsystems.com
RE: Balcony Collapse in Berkley, CA
I really don't see why not, but the point is that even if it only just works it has done its job.
If balcony rails are maintained, that's good. If the connection to the wall is removed (or replaced with one with insufficient strength) during maintenance that's bad, but the resulting system is no worse than the current standard design.
I will make some more general comments in the new thread.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
> way more fasteners
> way stronger wall
> way stronger flooring on the balcony
> way stronger railing.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
I doubt that the changes you listed would be required in the case of the balcony in question, but if they were one of the other options could be adopted.
Are you really suggesting that these structures have no practicable way of providing a secondary support mechanism that would prevent total collapse, or at least substantially reduce the risk?
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
I think Occam's Razor is being violated...
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
In some cases, yes. It's not that different that when we demand a certain failure rate, that we essentially have to duplicate the entire suite of hardware. The balcony in question has redundancy; what failed was not the redundancy, but the water intrusion protection; that was the weak link, not the joists. To demand an additional full redundancy would make the balcony way more expensive than it's worth in rent, and we would essentially restrict ourselves to buildings with no balconies, which would be a poor state of affairs.
Note that the lower balcony had ZERO water damage, which is what the design result should have been for the upper balcony. There have been several suggestions as to how that might have been accomplished, without resorting to redundant structures. There are balconies that have existed for centuries without failure, and without redundancy. To immediately demand redundancy seems to me to be a bit of a knee-jerk reaction.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
The blocking between the floor joist would not connect to them so they could act as the web of a T beam with the flange being 2- 3/4" plywood.Is this possible?
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
The point is that all structural systems have potential for significant degradation over time. Providing a secondary system to prevent total collapse in that eventuality does not need to cost as much as the original system, or anything like it.
As for the balcony having redundancy, I don't see any.
.
To suggest that redundancy is a totally impracticable requirement seems a bit of a knee-jerk reaction to me.
Provided that the redundant system does not reduce the reliability of the sub-system, then the overall reliability will be equal or better than the original system.
Not sure what the Occam's Razor reference is about.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
Yes. Though, what I was getting at is that (if you are going to open the can of worms) you have no choice but to assume the base system fails in its entirety (as the subject structure did), or else when something happens you have to explain why your belt and suspenders only has the belt and one suspender.
My reference to Occam's Razor is me suggesting that the redundant cantilever scheme may not be an elegant solution to the problem.
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
Yes, it is messy but uses a few bolts and hold downs and some blocking.
Would not the M be resisted by the HD7A tying into the dead load of the tributary floor and roof? The bolts into the wall might need bearing plates to spread the load.
Wouldn't the braced frame railing resolve into a couple of C=T at the interface of the stud wall, similar to a shear wall?I'd push for galvanized joist with weep holes in the bottom flanges and vent/ inspection holes.Any way you do it wood is messy and difficult to connect properly.
Inspector Jeff
RE: Balcony Collapse in Berkley, CA
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
"It is imperative Cunth doesn't get his hands on those codes."
RE: Balcony Collapse in Berkley, CA
Let's suppose that the balcony was only supported by the outriggers, and further suppose that a sensible design would have made each of the outriggers capable of supporting the entire load of the balcony. Then, by definition, there is redundancy. Since the balcony actually has 5 joists in addition to the outriggers, I think that meets the literal definition of redundancy. The fact that they all failed at the same, or nearly the same, time does not void the redundancy. Even if the railings had been a tertiary support, the same rot that affected the joists could have just as easily been located on whatever the railing might have been anchored upon, since each fastener requires penetration of the outer wall, and runs the risk of water intrusion.
My point is that there are always failure points; they're unavoidable. Even the redundancy professionals get it wrong sometimes, such as in the case of the DC-10 hydraulic systems, which were fully redundant, except at one specific spot in the tail, which was tolerably protected, until the rear mounted turbine developed a catastrophic blade failure, and took out all the hydraulics which had no cable backup, since it was nearly impossible, statistically, for all redundant hydraulics to simultaneously fail.
The issue is that redundancy is a slippery slope; where do you draw the statistical line in the sand, and can you live with the consequences when the line is crossed. Much of redundancy reliability is tied to the statistical analysis of probability of occurrence. So, even in the best case, an unknown probability can be assigned a lower value than what is real. Or, equally likely, the probability is correctly remote, but that probability card just shows up in the deck.
Case in point, and even considering the other balcony failure just reported, what is the statistical likelihood of a balcony failure? Is it one failure per million balcony-hours, or one per billion, or even trillion? Would any seriously contemplate potentially doubling the cost of a balcony to prevent a one in a billion balcony-hour failure probability? What about all the other one in a billion balcony-hour failures? Do we protect against them as well? The balcony-hours as I use it here is the number of actual balconies multiplied by the number of hours, so assume the the US as 70M housing units and 1/100 have a balcony, and assume there is one balcony failure every 2 years would result in 1 per 12 billion balcony-hours as the failure rate.
TTFN
FAQ731-376: Eng-Tips.com Forum Policies
[IMG http://tinyurl.com/7ofakss]
Need help writing a question or understanding a reply? forum1529: Translation Assistance for Engineers
Of course I can. I can do anything. I can do absolutely anything. I'm an expert!
There is a homework forum hosted by engineering.com: http://www.engineering.com/AskForum/aff/32.aspx
RE: Balcony Collapse in Berkley, CA
Take a car. It makes a lot of sense to me to have a traction-control system. Divert power from wheels that are slipping to those that aren't. Good redundancy.
But you can't do it everywhere. You wouldn't mandate a fifth wheel just to provide redundancy in case the four wheels stop working. That doesn't make sense. Those first four wheels just need to be engineered to work.
Same with this balcony. Providing a second load path is good when you can do it smartly. But this cantilevered system just needs to be engineered to work.
I agree with much that's said here. A few thoughts:
"We shape our buildings, thereafter they shape us." -WSC
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
So, we are all agreed then
On the basic principle, if not the application to a particular class of structures.
I do note however that there is a good deal of what I call either-orism in this thread.
Those who think additional redundancy in balconies is a good idea think the cost would be trivial, and those who think it would be a waste of time think it would be horribly expensive.
Funny that.
Doug Jenkins
Interactive Design Services
http://newtonexcelbach.wordpress.com/
RE: Balcony Collapse in Berkley, CA
RE: Balcony Collapse in Berkley, CA
If the designer knows all about this, why not use this to design the primary structure so it doesn't fail?
The belt-and-suspenders concept is appealing until the realization that neither belt or suspenders are under much load and that well fitted pants will stay up without either.
Regardless of cost, designing and building a structural back-up is very difficult, particularly to offset a basic deterioration unrelated to structural use. Even designing a structure to fail gracefully under overload when the parts are in like-new condition is hard.
RE: Balcony Collapse in Berkley, CA
It is easy enough to look a failure and determine the cause. How we react as an industry is what matters. There were a series of things leading to the final catastrophe. A fault tree would be useful, but I don't feel like drawing right now, so below is a ludicrously over-simplified assessment of how things got to where they are now:
failure: balcony fails due to deterioration of multiple structural members arising from undetected (or uncontrolled) water intrusion over a period of time.
Anywhere along the road to failure, this could possibly have been avoided. Some controls work better than others:
If the water intrusion had been properly prevented
If the effects of water intrusion had been mitigated
If the materials used were not subject to water damage (treated lumber or other material selection)
If the engineer had recognized that water intrusion was likely and specified appropriate materials
If the water intrusion had been detected and fixed
If the builder and his personnel had known about this issue and been more careful
If the owner or architect had required special inspection of the waterproofing
If the engineer had added separate redundant load path not subject to water damage from the same leak(s)
(aka If the structure was redundant enough, in the right ways)
If the building had not been built because they could not afford to construct a building costing more than one designed to minimum requirements.
RE: Balcony Collapse in Berkley, CA
Will be interesting to see how many balconies start disappearing in Berkeley because no one will sign them off as being "free from..."
Remember - More details = better answers
Also: If you get a response it's polite to respond to it.