Exterior Suspended Ceiling Code Requirements

Exterior Suspended Ceiling Code Requirements

Exterior Suspended Ceiling Code Requirements

(OP)
Looking at a 2' x 4' suspended ceiling panel system placed as a soffit on the exterior of a building. Ceiling failed in high winds. It was obvious there were no uplift struts. Going to court and need to cite all codes discussing the requirements. I found ASTM c-635. i have the 2003 version. Has this changed? Also, need additional codes if any as well as manufacturer's requirements.
Thanks

RE: Exterior Suspended Ceiling Code Requirements

ASCE 7 would provide the loads required on buildings. It has overhang uplift forces (for Components & Cladding wind).

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Exterior Suspended Ceiling Code Requirements

(OP)
Hoping to find something more specific on the drop ceiling to address up-lift.

RE: Exterior Suspended Ceiling Code Requirements

Well then read ASCE 7 - it is all in there. What do you want me to do, calculate it for you?

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Exterior Suspended Ceiling Code Requirements

Sorry for the snippy reply - been that kind of Monday...

The building code in the area (I'm assuming the IBC) will reference out to ASCE 7 which outlines all the required wind loads to be applied to buildings.

ASCE 7 has specific guidance on wind uplift for both open buildings and for overhangs of roofs. The Components and Cladding forces given in ASCE 7 would be used as the basis for the required uplift pressures on your ceiling. That is all there is to the wind uplift provisions.

If the ceiling failed by getting blow up into the roof (as you suggest - no uplift clips) then the system was obviously not designed properly to account for the wind.

I'm not aware of any other ASTM type documents that would apply here - you have a wind uplift pressure, you have a ceiling, the ceiling needs to account for the uplift.

Check out Eng-Tips Forum's Policies here:
FAQ731-376: Eng-Tips.com Forum Policies

RE: Exterior Suspended Ceiling Code Requirements

(OP)
Well aware of ASCE 7, use it all the time. Looking for something more such as ASTM C 635 Standard for Metal Suspension Systems. I found some stuff in FEMA Being harassed by lawyers and need to bury them in references.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close