Most times the instruction books and procedures provided by the OEM are not written to be performed verbatum, but should be used as guide lines by a person familiar with the entire plant (or at least the systems interrelated for a particulair event)
The instructions provided by the turbine OEM may not consider what type of device is being driven and thus how to include the driven must be decided upon by the plant. several have posted (and I have been involved with) that mechanical drive turbine instruction for the overspeed do not state the driven must be physically uncoupled. I have been questioned by several plants about requesting to seperate a feedpump from the turbine because neither supplied manual actually states to do so, My reply is that I am there for the turbine and have nothing to do with pump and refuse to allow it to "ride along" during over speed. and luckily the generations of designers before me included a method to seperate the two!
I must agree with racookpe1978 in that if must ask, you should not make any recomendations about how to perform these test, but seek the recomendations of someone knowledgable. the recomendation I have provided is what I have experance on a particular designed configuration. I hope you looked at the slideshare of the over speed test gone wrong.
BTW what is T/M? I'll assume revolutions per minute. given the couple values provided, am I correct in that your system frequency is 50 hertz with the turbines rated speed about 6425 rpms?