test oversped
test oversped
(OP)
Hello. When we want to do a test of the turbine overspeed us default Overfrequency trigger off in keep mode voltage regulator on.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Contact USThanks. We have received your request and will respond promptly. Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting Guidelines |
|
RE: test oversped
If you are asking about performing an actual over speed where the generator is NOT tied to the grid and the speed is increased above rated, then generator excitation is normally removed prior to accelerating above rated speed
RE: test oversped
RE: test oversped
I've seen plenty of thoroughly destroyed machinery, but never for such an obviously silly reason as this one!
Mechanical over-speed governors are normally tested on a test stand rather than on the turbine.
Valuable advice from a professor many years ago: First, design for graceful failure. Everything we build will eventually fail, so we must strive to avoid injuries or secondary damage when that failure occurs. Only then can practicality and economics be properly considered.
RE: test oversped
Here is the original message.
"Hi, I am an automation expert and we have a turbine siemens the question is when we want to do a test turbine overspeed it triggers a default of over-frequency programmed in siprotec 4 .the tie circuit breaker is open and the voltage regulator remains in mode on"
RE: test oversped
I would suggest googling "Eskom Duvha Unit No.4 9 February 2011" to view some photos of an overspeed test gone bad.
intersting finding, when I googled to verify the first hits would find the slide show, there was a recent news report where another accident occured at that station
RE: test oversped
if this is the case, this is a special feature only included if asked for at design stage...
"If you want to acquire a knowledge or skill, read a book and practice the skill".
RE: test oversped
A lot of insurance companies require testing of overspeed once a year as part of regular maintenance. Many OEM require it after major overhauls with turbine/compressor blade replacement. Normally the mechanical overspeed is done installed on the turbine, though can be done in the spin pit, if during an outage it can be removed and tested. I have never worked on a turbine, gas or steam that did not have a built in test program to conduct a "live" overspeed test. I personally have live tested dozens of electrical and mechanical overspeed tests at 3300 and 3960RPM
RE: test oversped
Johnny Pellin
RE: test oversped
RE: test oversped
RE: test oversped
The instructions provided by the turbine OEM may not consider what type of device is being driven and thus how to include the driven must be decided upon by the plant. several have posted (and I have been involved with) that mechanical drive turbine instruction for the overspeed do not state the driven must be physically uncoupled. I have been questioned by several plants about requesting to seperate a feedpump from the turbine because neither supplied manual actually states to do so, My reply is that I am there for the turbine and have nothing to do with pump and refuse to allow it to "ride along" during over speed. and luckily the generations of designers before me included a method to seperate the two!
I must agree with racookpe1978 in that if must ask, you should not make any recomendations about how to perform these test, but seek the recomendations of someone knowledgable. the recomendation I have provided is what I have experance on a particular designed configuration. I hope you looked at the slideshare of the over speed test gone wrong.
BTW what is T/M? I'll assume revolutions per minute. given the couple values provided, am I correct in that your system frequency is 50 hertz with the turbines rated speed about 6425 rpms?
RE: test oversped
RE: test oversped