I have a question about Air Testing of storage tanks. API 650 Annex F.4.4 calls for testing of vents during or after the Air Test. See extract below:
F.4.4 When the entire tank is completed, it shall be filled with water to the top angle or the design liquid level, and the design internal air pressure shall be applied to the enclosed space above the water level and held for 15 minutes. The air pressure shall then be reduced to one-half the design pressure, and all welded joints above the liquid level shall be checked for leaks by means of a soap film, linseed oil, or another suitable material. Tank vents shall be tested during
or after this test.
Pressure and Vacuum Relief Valves and Emergency vents have set pressures lower than the test pressure. If you want to test the vents during Air Test then you will have problems. The valves would open before you can reach the test pressure. Probably you can test the PVRV and then remove it (blind the nozzle) and then raise the pressure to go to set point of EV and ten remove EV and blind it and then go up to the tank test pressure. Is that how you do?
F.4.4 When the entire tank is completed, it shall be filled with water to the top angle or the design liquid level, and the design internal air pressure shall be applied to the enclosed space above the water level and held for 15 minutes. The air pressure shall then be reduced to one-half the design pressure, and all welded joints above the liquid level shall be checked for leaks by means of a soap film, linseed oil, or another suitable material. Tank vents shall be tested during
or after this test.
Pressure and Vacuum Relief Valves and Emergency vents have set pressures lower than the test pressure. If you want to test the vents during Air Test then you will have problems. The valves would open before you can reach the test pressure. Probably you can test the PVRV and then remove it (blind the nozzle) and then raise the pressure to go to set point of EV and ten remove EV and blind it and then go up to the tank test pressure. Is that how you do?





RE: Air Testing of Storage Tanks to Annex F.4.4
RE: Air Testing of Storage Tanks to Annex F.4.4
Much simpler and safer to fill at least 3/4 full and add air pressure to achieve the required test pressure.
RE: Air Testing of Storage Tanks to Annex F.4.4
Anchors are not required in my case. The question is about the practice. How do you comply with API 650 F.4.4 in terms of testing the vents. API states- Tank vents shall be tested during or after this test.
Do you test the vets?
Do you test them during the Air Test
Do you test them after the Air Test?
I understand that the Emergency Vent and PVRV will come tested from shop.
Thanks.
Ashok
RE: Air Testing of Storage Tanks to Annex F.4.4
*this assumes that these devices are from a reputable company and are intended for, and certified for, tank venting. My favorite mfr's are Protectoseal, Shand & Jurs, and Groth. [and yes, these are all North American companies; my experience isn't all that wide]
RE: Air Testing of Storage Tanks to Annex F.4.4
Carlos Molina from http://www.apiexam.com