Maintenance/Operation of ACSS Conductors

Maintenance/Operation of ACSS Conductors

Maintenance/Operation of ACSS Conductors

(OP)
Hello,
Does anyone have any experience using "hot-stickable" connectors for ACSS conductor? Generally you are required to use compression connectors for ACSS, but that significantly limits your ability to operate and maintain a line.

For example, you have a tap structure off of a ACSS line with a air switch on either side. If you want to perform maintenance on either switch, you must take the tap (and subsequent substation) down. Is there any connector out there for ACSS that is removable with a hot-stick so you could remove jumpers on one side of the tap structure to keep the sub operating?

Thanks
Replies continue below

Recommended for you

RE: Maintenance/Operation of ACSS Conductors

Put in line switches?

RE: Maintenance/Operation of ACSS Conductors

Providing a switch so you can maintain another can sometimes be an unending cycle, as you continue to add maintenance items. No compression stirrups for ACSS?

RE: Maintenance/Operation of ACSS Conductors

(OP)
Stevenal,
I'm not 100% sure what you mean by stirrups, but I Googled it and couldn't find anything for ACSS. How do you use stirrups for non-ACSS conductors?

RE: Maintenance/Operation of ACSS Conductors

A stirrup provides a place to land a hot tap. Any mechanical or arcing damage from installing or removing the mechanical tap takes place at the stirrup instead of the main conductor. A quick look at at http://www.te.com/us/en/industries/energy/pdf/Conn... suggested they consider their system suitable for all types of aluminum conductor including ACSS. Stirrups are on page 14. Perhaps you can find suitable compression stirrups as well, but you might want to check with the manufacturers regarding your use.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login



News


Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close