floor elevation compound

floor elevation compound

floor elevation compound

(OP)

What particular floor elevation compound do you use to make the floor or tiles higher? In my country. 100% of construction use sand mixed with cement as the filler. See the following picture:

http://www.pbase.com/rele/image/153741119

The tiles and sand elevation load is this.

15 kn/cubic meter x 0.05m = 0.75 Kn/m^2

The beam would have additional 0.75x20 = 15 Kn.

Do you think 0.75 KN/m^2 Superimposed Dead Load for a floor is low or high? what load do you typically use? And would elevation compound even be lower in weight? how low in square meter?

RE: floor elevation compound

A sand and cement thickset will weigh more that that. We typically use 24 kN/m^3 for concrete, and I think the sand/cement mortar would approach that density. What you have described is not uncommon for commercial construction with terrazzo tiles, marble tiles, etc. The actual setting method is something engineers are not so much involved in, as the trades have developed their own knowledge of what works and what doesn't. Saying that, there are examples of both good and poor flooring finishes wherever you go, so the competence of the tradesmen varies a lot.

RE: floor elevation compound

(OP)
24 kN/m^3 is for concrete with fine and coarse aggregates (stones or gravels). If one use only sand and cement without stones (or gravels), the weight would be around 15 kN/m^3 only. Do you not agree with this?

RE: floor elevation compound

No, I don't agree. I always use 24 kN/m^3 for mortar, terrazzo, or ceramic tiles.

RE: floor elevation compound

(OP)
I'm excluding the tiles for the 15 kN/m^3 but just the mortar. Let's break it down. What is the contribution of each to a concrete mix?

Water = ?
Sand = ?
Cement = ?
Coarse (stone) aggregates = ?

They should total 24 kN/m^3. But if you didn't include the coarse (stone) aggregates. Then a cubic meter should weight less. Why do you say it's still 24 kN/m^3? A cubic meter of sand is 13 kN/m^3. So add cement and few water and a cubic meter of concrete without coarse aggregates should weight about 15-18 kN/m^3.
Please elaborate details of where I analyze it wrong.

RE: floor elevation compound

If you don't believe me, just make your own samples and weigh them. It is the combination of materials that you want the density of, not the component parts. I think your sand density is low...19 is what I have used.

RE: floor elevation compound

(OP)
Anyway. For just supporting tiles that require only very little compressive strength. Do you know of more lightweight compound like perhaps plastic? What are other possible substances to be put under the tiles just to elevate it a bit.. maybe even wood can be used?

RE: floor elevation compound

Releky- why are you starting another thread on the same subject, when you got lots of input on it already?

http://www.eng-tips.com/viewthread.cfm?qid=356275

And my friend, if you honestly cannot figure out how to calculate dead load of floor toppings, you have bigger issues. You need a mentor engineer with local knowledge.

And what is with your superstructure design that it cannot handle the locally-used method of floor topping? The design should not be cutting it that close. The best floor leveling systems for floor tile, IMO, are self-leveling cementitious compounds (but they are expensive), or the method you posted would do the job. Wood is a bad idea usually because of moisture-related problems.

RE: floor elevation compound

(OP)
I'm trying to figure out how to mix low-density concrete that can make it only 1/3 the weight of structural concrete which is 24kN/m^3.. so for 0.05m (2 inches) low density concrete of tile elevation, it is about 24kn/m^3 x 0.05 = 1.2 kN/m^2. I'd like to make it only 0.4 kN/m^2. In structural books, they mentioned about light weight concrete that is only good for insulation (about 8kN/m^3 or 50 pounds per cubic foot).. but the books never mentioned how exactly to mix it... now i'm looking for a compound that is even lightweight like only 0.2 kN/m^2. Something like lightweight plasticize liquid just to support the tiles and typical live load. Since no one mentions of this exact plasticized compound. I post it again. So how do you mix low-density concrete that is only 0.4 Kn/m^2? I have tried using volcano tuff with very few cement and water just to bind it enough (actually my country use this technique) and I wonder if there are techniques to make it even lower in weight (what ingredients to add)?

RE: floor elevation compound

In the US lightweight concrete is usually made by using lightweight aggregate in lieu of gravel. As I understand it the lightweight aggregate is slate that has been put into an industrial "popcorn popper". Concrete made using this method is usually on the order of 120 psf = 19 kN/m^3 if I've done the conversion properly.

RE: floor elevation compound

(OP)
Archie, when you mentioned "lightweight aggregate".. are you referring to fine or coarse aggregates that are in lieu of gravel? What if all aggregates use is fine? Note lightweight aggregate include coarse aggregates. What would happen if all aggregates use is fine (super lightweight concrete), and there is less water and less cement just enough for cohesion and used just to support the tiles and 50 psf live load (which requires only mortar compressive strength of 0.5 psi (50/144)). How low the weight of this mix decrease? (15kN/m^3?)

RE: floor elevation compound

(OP)
cvg.. it's great product.. unfortunately it's not available in my place to buy in the thousands of bags.... so how does one make such kind of product? What other ingredients do you add to cement and sands to make it low density.. something like an expanding plasticized soda? What ingredients have anyone actually tried (those without access to such commercially available product)?

RE: floor elevation compound

releky and cvg

If my math and conversion are correct 3 lbs at 1/2" thick per square foot work out to 72 lbs. per ft^3.

That gives 11.3 kN per m^3. Better but no where near 0.2 kN per m^3.

Jim H

RE: floor elevation compound

(OP)

If you will check my message again. I mentioned "0.2 kN/m^2", not m^3. To make it m^3, change 50mm (approx 2") to 1 meter so multiply 0.2 by 20 to make it 4Kn/m^3. So I'm looking for a special plastic compound that is only 4kN/m^3 instead of the normal concrete 23kN/m^3 which I don't need this much compressive strength. I'm sure chemists can synthesize such. Meanwhile, What I do is use volcano cinders as fine aggregate, mix it 5 bags to 1 bag cement and little water just enough to cause cohesion. This would be controlled honeycombs but have enough compressive strength for the tile and live load. If anyone has done something like this, please share the technique. I want to make it even lighter by including plastic compound.

RE: floor elevation compound

Releky...adding coarse aggregate usually reduces the density (and thus, the unit weight) as compared to a sand-cement mortar, unless the coarse aggregate has a specific gravity greater than the sand specific gravity....bottom line, hokie66 is correct.

RE: floor elevation compound

releky,
You are contemplating the impossible. If my car only weighed 100 kg instead of 2000, it would use a lot less fuel. But that won't happen, and neither will your gravity defying levelling compound.

RE: floor elevation compound

(OP)
Huh? I don't understand what you are saying. Let me type the following for context of what I read in a reference on "Design of Concrete Structures" (note I'm basically just discussing of one creates low-density concrete):

"A variety of lightweight aggregates are available. Some unprocessed aggregates, such as pumice or cinders, are suitable for insulating concretes, but for structural lightweight concrete, processed aggregates are used because of better control. These consist of expanded shales, clays, slates, slags, or pelletized fly ash. They are light in weight because of the porous, cellular structure of the individual aggregate particle, which is achieved by gas or steam formation in processing the aggregates in rotary kilns at high temperature (generally in excess of 2000F). Requirements for satisfactory lightweight aggregates are found in ASTM C330, "Standard Specification for Lightweight Aggregates for Structural Concrete.

Three classes of lightweight concrete are distinguished in Ref. 2.2: low-density concretes, which are chiefly employed for insulation and whose unit weight rarely exceeds 50 pcf; moderate strength concretes, with unit weights from about 60 to 85 pcf and compressive strengths of 1000 to 2500 psi, which are chiefly used as fill, e.g., over light-gage steel floor panels; and structural concretes, with unit weights from 90 to 120 pcf and compressive strengths comparable to those of stone concretes."

Ok, so how do you create low-density concrete for insulation that rarely exceeds 50 pcf?

RE: floor elevation compound

hokie66...you realize we've been sucked in again from the same place!

releky....you clearly do not understand concrete technology, to include any cementitious material such as mortar, lightweight insulating concrete, lightweight structural concrete, grout or similar.

Just because you might be able to make a cementitious material lighter in weight does not mean it will work for your application. If you are going to put tile on the material, it has to be durable and has to have a reasonable compressive strength, and thus, a reasonable tensile strength to allow tile bonding and to withstand loading and cyclic movement.

Consider how poor your construction quality control appears to be, your floor slabs likely move a lot....therefore placing a lot of need on the mortar bed to be robust for the sake of the tile.

Yes...there are many lightweight aggregates available (mostly coarse aggregates). They are generally expensive and somewhat difficult to work with, but can be very effective in certain applications. This is not one of them. Just because you read something in a particular treatise doesn't mean you can grossly apply it to your situation without appropriate experience and judgment.

RE: floor elevation compound

(OP)

Quote:

If you are going to put tile on the material, it has to be durable and has to have a reasonable compressive strength, and thus, a reasonable tensile strength to allow tile bonding and to withstand loading and cyclic movement.

Yes, We have taken care of it. We use adhesive below the 2" of grout and above it and the tiles stick to it. This is used in 100% of hotels in our country which often has 2" of tile beddings. The reason the floors are not leveled is because traffic in streets usually makes the ready mix concrete come late and we have to hurry up to put it so the slabs are mostly not leveled with some parts higher. Traffic also caused many honeycombs in the columns of most hotels to form because it hardens fast and consolidation problems occur. It is solved by inserting fresh concrete but I think the old and new concrete are not really connected, so I believe that in the event of strong seismic movement, the columns moment magnification factor can go overboard with loss of moment of inertia. Now the subcontractor for tile don't know how to trim the high slab parts so they just call in the contractor to put mortal bedding. Note Laborers, carpenters, and masons in my country usually come from poor community so they don't have any skills but just know enough how to use hammer, nails, wood and mix concrete. We live in very poor third world country with daily wage of workers averaging just $8 (eight dollars) for 15 hours of work daily.

Anyway. Since we don't have the lightweight mortar compounds available commercially. I have to mix stuff and asking which can have the lowest weight. Again, adhesive below and above the mortars solve the problems of tensile strength, tile bonding, loading and compression strength. Note the compressive strength of the mortals don't have to be 4000 psi for example.. they just need to be good for 100 psf (4.8 Kpa) live load.

RE: floor elevation compound

I understand your issues and it is unfortunate that such construction is allowed to exist. It is a danger to the public.

I also understand that a mortar bed does not need a compressive strength equivalent to the strength of the structural concrete; however, it must have a compressive strength sufficient for durability of the application, which is greater than the 100 psf bearing that you noted. Bonding adhesive above and below the mortar bed does nothing if the mortar bed fails in tension or horizontal shear.

Learning more about concrete technology and mix designs will help you to counteract some of the difficulties of delivery time and concrete consolidation.

Remember...good concrete consists simply of cement, good aggregates and water. Unfortunately, bad concrete can consist of the same ingredients.

RE: floor elevation compound

releky,

I stand corrected. That gives us 11.3 kN per m^3 still no where near the desired 4 kN per m^3. In college for the concrete canoe contest we made floatable concrete, less than 62.4 lbs per ft^3 or 9.8 kN per m^3 with a glass bead aggregate. But it wasn't very strong so we used half gravel and sand and half glass bead aggregates that worked but still wasn't very strong and was nowhere neat 4 kN per m^3. I don't think you are going to find a suitable aero-gel aggregate.

Jim H

RE: floor elevation compound

(OP)

After spending time with the tile installer. I learnt how exactly they do the proportion of the mortar bed mixing and this is how the millions of buildings in the country are done. Here's how. It's 1 part cement and 2.5 parts sands. But the water added is very few just enough to wet the mix. So the texture of the final mix is not paste-like but soil-like (rough), the reason for this is so they can level the tiles, because it's harder if the bedding is paste like. This works well because it's also what's done in hotels and all buildings in the country. Note adhesive is added above the mortar bed and below for adhesion of the tile.

I weight the mix in one square carton and 1 inch thick. It's roughly 87 Lbs/feet^3 or 13.6 Kn/m^3. It doesn't reach 23.56 Kn/m^3 because the lack of enough water prevent complete adhesion into paste-like texture (meaning there is microscopic aid voic). But the final mix is strong enough to take 100 lbs/feet^2. Remember this is done in all buildings in the country.

Now my question is. If there is not enough water in the mortar mix. And the hydration of the cement is just partial. Would it continue to hydrate when water gets into the bedding (let's say months later)? I need to know this important because I don't want hydration to continue months later and the weight to become more (would it?) Remember the water in the chemical reaction with the cement form the final weight of the concrete. So any water seeping to the bedding may continue the hydration. What is your opinion?

RE: floor elevation compound

If the mortar weighs only 87 lb/cu ft, it is very porous. Therefore, it will be a reservoir for any water which infiltrates. Whether or not it hydrates cement depends on how much cement remains to be hydrated.

RE: floor elevation compound

Based on the photograph and the description, and like I said on the previous post on the same topic, this appears to be "mud bed" or "thick bed" installation, and is basically the Old World method that has been used for hundred if not thousands of years (in different versions). This is still very common in Spain in my experience.

It seems to work very well to level the floor and also does not directly bind the tile to the floor, so it is uncoupled, and therefore cracks and movements of the floor slab do not necessary transfer the stress into the tile assembly. Having inspected tile failures and experienced them first hand with my own property, the failure is due to long term moisture expansion of the tile which fails the mortar bond to the concrete slab in shear and tension. I do not think this is as critical with thick bed installations as described because the tile is not bonded directly to the rigid slab, the sand-cement mixture provides a slip plane for the tile. Though you could still have problems in long tile runs like hallways or large rooms if you do not have expansion joints. Also depends a lot on the tile.

But the poster said they use some type of adhesive to bond the tiles to this layer. I wonder if this is still done while the mud is still green?

Some info here:
https://www.tcnatile.com/faqs/65-mortar-bed-compre...
http://en.wikipedia.org/wiki/Thick_bed_mortar

Anyway, back to the topic at hand. If this is typically how tile is installed in your locality, then the structure should have been designed for this dead load. There is not much you can do to the weight of sand, cement and water to make it weight less, as Hokie has indicated.

It sounds like you (releky) are a field/site engineer, and as such it is not your responsibility to re-engineer the building as it is being constructed. If you go away from the tried and true methods, what if you have tile failures? Will you be held responsible?

Have you been discussing these issues with the structural engineer who designed the building?




RE: floor elevation compound

(OP)

Yes, the adhesive is put below the mortar bed and between the tile and mortal while the mortal is still wet. Again, it's not paste-like texture like in structural concrete pour but soil like texture. The tile installer didn't compact the soil-like mortal. What they do is level the soil mortar to the height of the neighboring tiles. Then use the wooden side of hammer to notch the tile until it goes deep enough to be same level as the other tile. Btw.. the tile is only 8mm in thickness synthetic granite, china made. So for 2" soil-like mortar bedding with 1 cement part to 2.5 sands part (white sands) and little water just to wet it, and only 8mm compact space (the thickness of the tile insert), I wonder how big is the pores inside (akin to honeycombs). I'm looking for a molecular software to simulate the density and effect. And noting that water has specific gravity of 2.32, it shouldn't add so much weight.

Also please confirm if the following analysis is correct. When you add water to sand/cement mortal mix. The purpose of the water is not only for chemical reactions or hydrations of the cement and water and binding with the aggregates and workability, but putting water has effect of making the sand particles bind closer. So in the finished 2" soil-like uncompacted bedding with many pores, putting water can't make the unhydrated cement become large in volume that can fill the pores. So water infiltrates months later won't make the 13kN/m^3 porous mix to become 23kN/m^3. Agree with this?

Yes. I'm a field engineer and the designer said to make it as thin as can be but if not possible, then thick.. this is what every designer of all buildings in my place think... the flooring being part of Superimposed Dead load. I just want safe allowance and can change tile bedding mix if I think it's necessary.

RE: floor elevation compound

"And noting that water has a specific gravity of 2.32,..." That would be...wrong!

RE: floor elevation compound

On a raised floor slab with tile on it, where is this excess water coming from?

Seems like you are over-thinking this. Keep the dead load under what the drawings state or what the structural engineer said he designed it for, and let the tile guy do what tile guys do in your area. You should have an engineer in your locality who knows all these things and can help mentor you....

RE: floor elevation compound

(OP)
I meant concrete has specific gravity of 2.32

I asked the tile installer why he has to use soil-like texture. He said before they used typical concrete paste-like mix and what happened was that after a few years the tiles rise up with respect to other tiles. What is the cause of this? The tile installer doesn't know since he is not familiar about hydration. He said all the country tile installers use the technique used in Saudi Arabia or soil-like texture mortal bedding due to the problem encounters decade ago.

Now what would be the advantage if the soil-like texture mortal bedding is thicker as one of you (a2mfk) mentioned it has advantage (note what I meant by "soil-like texture mortal" being due to not enough water to turn the 1:2.5 cement sand into paste as I explained previously)

The designer is not familiar with such tile installer details. He used told me to use the thinnest as much as possible or the lightest and learn how to do it and decide what to use and so I need to know the technique used by tile installers.

Also what would happen if the tile is just attached using adhesive directly to the floor? Isn't it the rest of you use this? won't you encounter any rised tile or crack?

RE: floor elevation compound

I have used lightweight concrete on metal deck to help reduce building mass in high seismic zones. BUt I have never used lightweight mortar to make the superimposed tile load less because the building can't take the added gravity load...

This is funny stuff... LOL

RE: floor elevation compound

(OP)

After long consultation with the designer. He told me he actually didn't consider tiles and thick toppings in his calculations which is very tight owing to steel prices very high. After consulting with other designers. We decide to remove the tiles (it is already fully done). But we can't use bare slabs for foot traffic. Can anyone recommend what other lightweight flooring (maybe wood) available? What synthetic flooring is available and what synthetic copolymer compound to use (we need to rise it 2" thick for proper elevation). Thank you.

RE: floor elevation compound

You are in trouble if the engineer did not allow enough dead load for tile and a mortar bed. Do you not have a boss who is an engineer who has a lot more experience with local practice and can help you?

What dead load did the engineer provide for flooring installation? Wood flooring can have significant weight and wood in general is not very effective for leveling. The leveling compounds I am familiar with are expensive and not lightweight.

Tile "tenting" is mostly commonly caused by a failure of the mortar bond in shear due to long-term non-reversible moisture expansion of the tiles. Each tile expands slightly, generating compressive forces in the tiles, and if the mortar bond fails, the tiles relieve the compressive stress by tenting upwards. All ceramic products being to absorb moisture after they leave the kiln, some more than others. An exacerbating factor would be shrinkage of the slab.

RE: floor elevation compound

(OP)
Here's the layout of the property



http://imageshack.us/photo/my-images/138/qwqv.jpg/

The designer said he made a mistake and there is only 164 kN capacity in the middle horizontal girder. All the beams are 0.5 depth by 0.3 width. There is sufficient longitudinal rebars but stirrups in the middle are only 0.2 m apart while at the sides it's all 0.1 m. Bottomline is, he used the analysis of triangular shear and realised after construction (after checking everything) that the shear should be constant from the middle to the sides. So the present girder can't support additional superimposed dead load. So he added 80 kN by putting carbon fiber. There is carbon fiber installed last month. But you know carbon fiber are controversial. What if it won't work. Therefore I and another engineer can't trust it. The carbon fiber is supposed to support the tiles and 2" mortar bed and some live load. But FRP for shear is not tested. Therefore we can't take chances and need to make lighter mortar bed. The boss says ok to make it lightest. But he doesn't have any idea about lightweight flooring system.

Can you think of any plastic based mortar bed (say entirely synthetic plastic) that can make it say only 7 kN/m^3? Right now the mortar bed is about 15 kN/m^3. We want to deduct about 10 kN of mortar bed load to make it lighter. The owner said even if the floor system is not very good. It is better to be safe than worry. So no problem if cement mortar bed can take the movement of the tile better than synthetic plastic and has to be replaced often Btw.. I weight of the tile is only 1.5 (not typo) pounds per square foot (it is light being only 8mm thin) so the problem is the heavier 2" mortar bed.

RE: floor elevation compound

(OP)

I won't replaced the entire floor.. only the middle portion near the girder or the tributary area form by the secondary beam nearest to the center. I need to take off about 10kN of mortar bed weight. Is there just no synethetic compound (not composed of sand and cement) that is just 8kN/m^3 that can work with the floor with good misc. characteristics? Can't no such compound ever be fabricated or synthesized?

RE: floor elevation compound

(OP)

By the way, in many millions of buildings with mortar bedding. Many experience cracking after 3 years. What happened is that mortar bedding itself just rise up against the tile. So you can't say it is the tile that compresses against the mortar bed. Any ideas why the mortar bed cracks upwards? Is it because they did it so thin or the concrete so hard? The tile installers and most local engineers can't explain it.

Whatever, I think I have to invent synthetic plastic that can be make flowable so they can be poured into slabs acting as tile bedding with good compression, shear, tension and moisture control. If anyone has seen this. Please share it. If none. I think I need to invent it myself.. so need crash course in chemical engineering.

RE: floor elevation compound

With design engineers like the one you are describing, excessive deflection of the floor slab will put additional compression into the tile assembly. But tile tenting ultimately is a result of the mortar bond failing, in most instances this is due to poor surface preparation and/or workmanship issues.

Can you use vinyl flooring? Lightweight, durable, and can look like tile or wood. If you can get it where you are. But I know of no lightweight leveling compounds that also have good enough compressive strength to support tile.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close