Would someone advise a typical gradtion for backfill materials which would be free draining for behind the mse walls. The one spec says:
35-100 pass 19mm
15-60 pass 4.75 mm
3 to 15 pass 0.297 mm
0-5% pass 0.075 mm
It seems the above has too much sand encapsulating the gravel withing the sand and resulting in a low permeablity. Thanks.
35-100 pass 19mm
15-60 pass 4.75 mm
3 to 15 pass 0.297 mm
0-5% pass 0.075 mm
It seems the above has too much sand encapsulating the gravel withing the sand and resulting in a low permeablity. Thanks.
RE: Backfill gradation
Therefore the gradation you list would be free draining if placed adjacent to a silt or clay, but not free draining if placed adjacent to a clean gravel. Additionally you have to consider filter effects. The drain material needs to be either sized as a filter for the adjacent material or a filter needs to be provided.
Mike Lambert
RE: Backfill gradation
RE: Backfill gradation
As for you comment about clay adjacent to clay, very theoretical since getting a clay permeability that close would be very tough. However, if you could then the 10-6 clay would be free draining (i.e. dry) if the only source of water it had was from the 10-7 clay.
Mike Lambert
RE: Backfill gradation
RE: Backfill gradation
The challenge is whether to use pure gravel (e.g. 100% retained on 4.75 mm) or sand and gravel with <5% fines (e.g. river alluvium). A colleague believes that if we have 47.5% sand and 47.5% gravel and 5% fines, the gravel acts as a guest in the matrix and in fact the sand would be the media through which water would seep. Hence the % of silt in the soil, which is actually subject to seepage will be 10% of the weight of sand.
This would then imply that we would have dirty sand, the permeability of sand with about 10% fines would thus diminish, compromising the free drainage criteria. This seems a theoretical paradox but I am looking for an answer. Nevertheless that is the reason that I am searching on this subject.
RE: Backfill gradation
As for you question, I would not allow any significant amount of minus 200 materail in my drainage layer.
Mike Lambert