Calculation of DISTURBANCE FACTOR for Steam Blow out
Calculation of DISTURBANCE FACTOR for Steam Blow out
(OP)
Dear friends,
We want to remove sludge and debris of steam pipe lines by steam blowing method.
If we want to have a efficient steam out as it said before, disturbance factor must be higher than 1.2.
Normal operation condition of pipe line is:
Pressure :22 bar
Flow rate: 175 ton/hr
Temperature: 245 oC
we don't have enough steam to reach 1.2 by increasing flow rate and therefor only way is to decrease pressure to have higher specific volume.
I want know when we blowing steam to atmosphere, and we have 22 bar steam at supplied point, which pressure must be applied to calculate specific volume?( atmosphere?, supplied pressure?, average of them? or we must apply a pressure gauge to read real pressure? ( in latest case where gauge must be installed? near the outlet temporary line or inside loop?))
Also how much we can decrease the pressure to reach enough specific volume? is there any limitation? for example we will have 80 ton/hr 22 bar steam during steam blow out and we must decrease the pressure to 13 bar to have disturbance factor equal to 1.2. is it safe or may be we will face with strong hammering?
only way to decrease the pressure is using the supply valve (globe valve) to break down the pressure. is it the right method or not.?
I will be thankful for any early response.
We want to remove sludge and debris of steam pipe lines by steam blowing method.
If we want to have a efficient steam out as it said before, disturbance factor must be higher than 1.2.
Normal operation condition of pipe line is:
Pressure :22 bar
Flow rate: 175 ton/hr
Temperature: 245 oC
we don't have enough steam to reach 1.2 by increasing flow rate and therefor only way is to decrease pressure to have higher specific volume.
I want know when we blowing steam to atmosphere, and we have 22 bar steam at supplied point, which pressure must be applied to calculate specific volume?( atmosphere?, supplied pressure?, average of them? or we must apply a pressure gauge to read real pressure? ( in latest case where gauge must be installed? near the outlet temporary line or inside loop?))
Also how much we can decrease the pressure to reach enough specific volume? is there any limitation? for example we will have 80 ton/hr 22 bar steam during steam blow out and we must decrease the pressure to 13 bar to have disturbance factor equal to 1.2. is it safe or may be we will face with strong hammering?
only way to decrease the pressure is using the supply valve (globe valve) to break down the pressure. is it the right method or not.?
I will be thankful for any early response.
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out
You may have better options as our application is part of commissioning. There are a few contractors out there that have a lot of experience with different types of blows. I've only seen the type specific to our product.
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out
Thank for your reply.
But there is another question.
It seems that 2 methods applied to steam blow out. in firs method a sacrifice valve positioned at the end of pipeline and before temporary line ( valve must be quick open type) and after pipe filled with steam up to desired pressure, sacrifice valve will be opened and for some minutes (5-15 minute)steam is blown with maximum rate that boilers can provide without loss of water level at steam drum.
in second method, that is continuous, a low pressure steam with high flow is blown from pipe without any valve at the end of pipeline and after 1-2 hour supply valve of steam is closed and it is allowed till pipe line cooled and because of contraction and latter expansion , scaled and debris dislodged from pipe and this is repeated until we have a clean pipe.
in the first method if we install a pressure gauge at the pipe line we able to read constant pressure across the pipe but in second method we have a pressure profile that is high near the supply and is low near the outlet at temporary pipe. if we install a PG, where is the right place for installing ( start of loop, mid point or end point)?
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out
Thank for your reply.
But there is another question.
It seems that 2 methods applied to steam blow out. in firs method a sacrifice valve positioned at the end of pipeline and before temporary line ( valve must be quick open type) and after pipe filled with steam up to desired pressure, sacrifice valve will be opened and for some minutes (5-15 minute)steam is blown with maximum rate that boilers can provide without loss of water level at steam drum.
in second method, that is continuous, a low pressure steam with high flow is blown from pipe without any valve at the end of pipeline and after 1-2 hour supply valve of steam is closed and it is allowed till pipe line cooled and because of contraction and latter expansion , scaled and debris dislodged from pipe and this is repeated until we have a clean pipe.
in the first method if we install a pressure gauge at the pipe line we able to read constant pressure across the pipe but in second method we have a pressure profile that is high near the supply and is low near the outlet at temporary pipe. if we install a PG, where is the right place for installing ( start of loop, mid point or end point)?
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out
I'd be curious if anyone has any different experiences with the continuous method.
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out
We usually aim for a CFR of 1.15-1.2 at the outlet of the pipe. The higher pressure at the inlet will have a CFR slightly higher, but still within the acceptable range.
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out
Thanks for your reply.
We do a simulation with Hysys and it shows that after supply valve we have very negligible pressure drop across the pipe line and if we have 1.2 bar at the outlet to atmosphere we would have 1.5-1.6 bar after supply valve, because friction of pipeline and bends is only source for pressure drop. in this case specific volume isn't very different for .5 bar PD.
I surprised that it seems that we need only high flow rate and sufficient temperature to have 50-70 oC above saturation temperature. and we can do steam blowing with 5 bar same as 40 bar steam because in every case supply valve bring sufficient "delta P".
Can you approve this or you have other idea?
RE: Calculation of DISTURBANCE FACTOR for Steam Blow out