4 pole fused disconnect (for Europe) make any sense?

4 pole fused disconnect (for Europe) make any sense?

4 pole fused disconnect (for Europe) make any sense?

(OP)
I am working on a power distribution panel which will be marketed in Europe. The power line is 3 phase Wye. My group leader has asked me to research disconnect options. He asked me if we should use a 4 pole fused disconnect.

My gut tells me that you may not want to fuse neutral. Would I be better to use a 4 pole non-fused disconnect and a 3 pole fuse block with FRS-R125 fuses in order to meet code?

We are putting 4 pole breakers on the output. I figure current-limiting fuses would allow me to use output breakers with lower short-circuit ratings and save me a few bucks.


Thank you for your help.

Regards,
Bob
N9NEO

RE: 4 pole fused disconnect (for Europe) make any sense?

Just slug the neutral position.

RE: 4 pole fused disconnect (for Europe) make any sense?

Have a look and EN60204
As far as I recall disconnection of the neutral is mandatory in France and Norway for a TN-S system.

If you have a PEN conductor you do not want to disconnect the neurtal as it is also your protective conductor

Often manufacturers install a 4 Pole Disconnect and then allow the user to connect the "live" side of the neutral to earth using a removable link.
Make sure you instruction manual exlains how to do that.

If you go with a 3pole you would have to forbid use in a TN-S system and clearly state so in the manual

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members! Already a Member? Login


Resources

Low-Volume Rapid Injection Molding With 3D Printed Molds
Learn methods and guidelines for using stereolithography (SLA) 3D printed molds in the injection molding process to lower costs and lead time. Discover how this hybrid manufacturing process enables on-demand mold fabrication to quickly produce small batches of thermoplastic parts. Download Now
Design for Additive Manufacturing (DfAM)
Examine how the principles of DfAM upend many of the long-standing rules around manufacturability - allowing engineers and designers to place a part’s function at the center of their design considerations. Download Now
Taking Control of Engineering Documents
This ebook covers tips for creating and managing workflows, security best practices and protection of intellectual property, Cloud vs. on-premise software solutions, CAD file management, compliance, and more. Download Now

Close Box

Join Eng-Tips® Today!

Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.

Here's Why Members Love Eng-Tips Forums:

Register now while it's still free!

Already a member? Close this window and log in.

Join Us             Close