Can anyone explain to the difference between restricted and unrestricted earth fault relays.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Contact USThanks. We have received your request and will respond promptly. Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting Guidelines |
Restricted Earth Fault Relays
|
Join your peers on the Internet's largest technical engineering professional community.
It's easy to join and it's free.
Here's Why Members Love Eng-Tips Forums:
Register now while it's still free!
Already a member? Close this window and log in.
RE: Restricted Earth Fault Relays
One CT in the transformer neutral is balanced against the neutral of three phase CTs in the transformer output connection (or bushing CTs in the transformer circuit breaker) and connected in parallel. The REF relay is connected across the two CT leads - this relay is a high impedance type, operating on fault voltage developed across the CT leads for an internal fault. For an external earth fault, the zero sequence current in both sets of CTs is balanced and there is no fault voltage developed on the CT leads.
The REF scheme is a high speed differential protection, with instantaneous operation for internal faults and high stability (depending on setting) for external faults.
By extension, an unrestricted earth fault relay is a relay connected to a single CT or set of CTs to measure zero sequence current. This is a normal time delayed overcurrent relay, which must be delayed to coordinate with other relays downstream. This would normally be a non-directional relay, but could be directional depending on the application
RE: Restricted Earth Fault Relays
A. To peterb posting:
1. To the first sentence: The restricted ground fault relays provide more sensitive protection for the equipment (transformers or generators) internal faults to ground; not phase to phase (to phase). They are used to protect transformers rated at or over 10000kVA. Heavy external faults may trip this relay because of cts' asymmetries. To avoid this, additional choke, capacitor and short time delay (relay) 1 to 2 seconds are needed mitigate the effect of harmonics and DC component. Finally, a stabilizing resistor is connected in series with the relay. See page 181 of A. R. van C. Warrington "Protective Relays Their Theory and Practice" Volume I., 1971.
2. External faults are protected by another differential relay (Dev. 87), which is applied regardless of transformer 10000kVA size needed for the restrictive earthing relay.
B. To 140668: There is also a good reference IEEE Std 242-1986 "IEEE Recommended Practice for Protection and Coordination of Industrial and Commercial Power Systems."
RE: Restricted Earth Fault Relays
- The REF scheme requires matched CT characteristics on the phase and neutral; any mismatch in saturation voltage is taken into consideration by the use of a judiciously selected stabilizing resistor; the relay can be either a current relay, with an external stabilizing resistor, or a voltage relay with an integral resistor.
- The REF scheme setting is selected on the basis of the maximum votage developed at the relay for the worst-case external ground fault, taking the CT characteristics into consideration. Normal scheme setting is <50% of the CT kneepoint voltage.
- The relays normally used for these schemes include harmonic filters; these would not normally be provided external to the relay
- Time delays are not usually applied with this type of protection
- External faults outside the zone defined by the REF CTs require a non-restricted scheme as backup protection. Device 87 is a differential relay, with a defined protected zone - this will not operate for external faults.
The REF scheme is a subset of high impedance differential schemes, which are generally used for bus protection. An excellent reference is the Protective Relaying Application Guide, published by the former GEC Measurements (now Alstom T&D)
RE: Restricted Earth Fault Relays
RE: Restricted Earth Fault Relays
The REF scheme protects the earthed winding to which it is applied for internal earth faults, with a more sensitive setting than is possible with the transformer differential relay. The zones of protection for both 87TG and 87T on the protected winding are usually the same, with shared CTs, so that the 87T cannot be said to be protecting for external fault conditions.
RE: Restricted Earth Fault Relays
RE: Restricted Earth Fault Relays
1. While I agree that the IEEE standards are an excellent reference, they are intended to summarise elements of engineering practice, not to serve as design standards to cover all cases for all time. An example of the changes that have been made in accepted practice since the referenced date of 1986 is the introduction into general service of microprocessor-based transformer protection relays - these allow connection of the CTs on both sides of the transformer to be made in wye, with the required phase shifting and zero sequence current filtering being done internal to the relay.
2. Even prior to 1986, it was standard practice in the world outside of the IEEE standards for CTs to be shared between the transformer differential protection and the REF protection. This was done by the simple expedient of installing a set of carefully selected interposing CTs in the circuit. The transformer CTs on both the Delta and Wye windings were connected in grounded wye. The CT circuit from the Wye winding was then connected to the wye-connected primary of the interposing CTs, with the REF scheme connected to the neutral of this circuit. The interposing CT secondary was connected in delta, providing the necessary phase shift and zero sequence current filter for connection to the differential relay.
3. My experience has been that large generators are always unit connected and consequently are earthed using a distribution transformer/resistor combination. With this situation, earth fault currents are restricted to very low values and provision of a current-based earth fault detection scheme is inappropriate - earth faults are usually detected by neutral voltage measurement.
Anyway, 140668, I hope that all of this has helped to answer your original question, even if has been rather detailed.
RE: Restricted Earth Fault Relays
1. Switching to microprocessor relays is departing from the original posting. The microprocessor relays are often synthetized version of electromechanical relays with the substantial amount of sophistication and complexity imbedded in them.
2. There appears to be other solutions possible. My posting did not exclude those. I just do not see any references in the posting. Your statements seem to be reflecting your experience, which is fine.
3. The high-resistance grounding is limited by the voltage level and charging earth current. If those are not met, the medium resistance grounding or other grounding method is applied. That is where your "always" statement is misleading and inaccurate. The "final comments" are your prerogative since this is the public forum to address different views and elucidate topics without any contractual agreements.