I'll attempt to answer my own question. I'm trying not to make this a rant...but it is a little frustrating that there does not seem to be a clear cut YES or NO to this question. This wiring is to a PLC - one of the most common wiring situations on Planet Earth. There are fuses and circuit breakers protecting every circuit. I really don't understand why a lighting circuit is allowed per the NEC in some cases to operate with a #18, a small motor to operate with a #18 and yet a maximum of .020 AMP circuit, that's 20/1000 of ONE amp, has to use a #14 gauge wire except under the complicated rules of Article 725. If I'm missing something please help!
Here's the research I've done so far:
2011 NEC: 310.106 Conductors."(A) Minimum Size of Conductors. The minimum size of conductors shall be as shown in Table 310.106(A), except as permitted elsewhere in this Code."
And that size is #14 for Copper and #12 for AL conductors for conductors <2000V
I'm looking "elsewhere" if I can use anything smaller than #14:
240.4(D)(1) #18Cu is to be protected by a 7 Amp fuse...
240.4(E)(1) #16CU is to be protected by a 10 Amp fuse....
330.104 Conductors. MI cables allow to be made in #18AWG copper.
430.22(F) A less than 1hp motor in a certain situation can be fed by #18AWG
517.75 X-Ray equipment - Allows Size 18 AWG or 16 AWG fixture wires as specified in 725.49...where protected by not larger than 20-ampere overcurrent devices.
522.21(C) Permanent Amusement Parks - allows for #26AWG to be used multiconductor cables
600.31(B) Neon signs can use 18 AWG.
604.4 Manufactured lighting systems allows #18
610.12 Cranes and hoists: some wires can be #18 under conditions for circuits not operating at more than 7amperes. And electronic control circuits can be #20AWG.
620.12 Elevators and Dumbwaiters Article 620.12 allows travelling conductors to be 24AWG and even smaller if listed.
725.49 Allows for #18 Class 1 circuits
725.127 The supply side of a Class 3 transformer can be a #18
727 Instrumentation cable....specs for small wires and ITC cable, but WHY does it have to be ITC rated and meet all the conditions?
760.43 NPLFA Circuit Overcurrent Protection. allows for #18 is protected by a 7Amp fuse
760.127 The supply side of a listed PLFA Class 3 Fire Alarm transformer can be a #18