We have A 572 structural steel components of transmission towers welded then hot dip galvanized (Zinc coating). I would like to know which is the best NDE method to check weld cracks after glavanizing and why the method is good? Your responses will be greatly appreciated.
We have A 572 structural steel components of transmission towers welded then hot dip galvanized (Zinc coating). I would like to know which is the best NDE method to check weld cracks after glavanizing and why the method is good? Your responses will be greatly appreciated.
RE: NDE Inspection of welds after galvanized.
Steve Jones
Materials & Corrosion Engineer
http://www.linkedin.com/pub/8/83b/b04
All answers are personal opinions only and are in no way connected with any employer.
RE: NDE Inspection of welds after galvanized.
Check out this link
http://elsa.jrc.ec.europa.eu/publications/JRC56810...
Regards
RE: NDE Inspection of welds after galvanized.
Best regards - Al
RE: NDE Inspection of welds after galvanized.
It depends upon how thick the coating of galvanize finishes up to be.
RE: NDE Inspection of welds after galvanized.
If a weld is covered with galvanising how do you inspect it ?
The structures should be rejected, NCR raised, welds blasted, tested then re-galvanised.
Regards,
Kiwi
RE: NDE Inspection of welds after galvanized.
A magnetic particle test using an AC yoke and dry particle seems to be doing a pretty good job of detecting the cracks in the radius of the access holes and other thermal cut surfaces after HDG. Since there has been a problem identified, a number of fabrictors routinely perform the MT in the areas of concern.
I have not been asked to do UT, but I am confident pulsed echo UT with a 70 degree wedge would find the cracks as well, but MT seems to be working and it is less expensive.
Best regards - Al
RE: NDE Inspection of welds after galvanized.
I may be barking up the wrong tree here and it may be exactly what you are commenting on.
However, my understanding of the initial post is they have neglected to perform required NDT prior to galvanising and now are looking for an "out" so they don't have to remove the galvanising and perform the required tests,
Cheers,
Kiwi
RE: NDE Inspection of welds after galvanized.
Back to my comment; the members involved exhibited no evidence of cracking in the area of the access holes or the copes and blocks before HDG. However, after HDG some cracks were large enough to be seen. The MT was used to check all the steel after HDG and low and behold, cracks were identified using MT after HDG.
The sensitivity of MT is reduced as the thickness of the coating increases, but MT with an AC yoke seems to be working with the normal thickness of HDG coatings. Whether the test is sensitive enough to satisfy your needs you can easily validate the MT by putting different thicknesses of plastic film on a sample of steel to see if you can still detect the crack.
Best regards - Al
RE: NDE Inspection of welds after galvanized.
The part was not split like that before it was placed in the zinc tank.
Bill
RE: NDE Inspection of welds after galvanized.
Here are a copy articles, though several years ago, that may be helpful:
http://www.aws.org/itrends/2005/10/023/
http://www.aws.org/itrends/2004/07/it0704-29.pdf
Another technique that works well is ACFM. ACFM is routinely used to inspect surfaces beneath coatings. One of the systems that I have used was the Lizard ACFM M8 NDT System.
Richard www.6sproductivitycom.com