History of secondary voltages in US
(OP)
I am writing an article and I would like to find out if there is some history (real numbers) of secondary voltages in the US. That is voltages actually supplied to the home. I know we started out at 110 DC and then 110 AC but over the years this has crept up to now in many area 120+ (often 123 or more) is very common. Much older equipment, say before 1930 or so had 110 voltage nameplates and later equipment was often designed around 115 or 117 volts.
What I would like to find out is how these voltages were increased over the years. Was it a gradual increase or were there steps and if so when. Have there been any papers written non this or is there historical data that can be viewed? Or it might just be an old timer that remembers! I also realize that this is often power company dependent but I am looking at averages.
What I would like to find out is how these voltages were increased over the years. Was it a gradual increase or were there steps and if so when. Have there been any papers written non this or is there historical data that can be viewed? Or it might just be an old timer that remembers! I also realize that this is often power company dependent but I am looking at averages.





Talk To Other Members
RE: History of secondary voltages in US
I have seen old appliances rated at 100 Volts and 105 volts. 110 volts became standard. Companion voltages were 220 Volts and 440 Volts
I remember reading (and I have been looking for the reference for decades now) that a decision was taken to increase the voltage to 150 Volts. This was to be done at the rate of 1/2 Volt per year. That was a good choice considering the expected life of distribution transformers of the day. This may have started in the 40's probably after the war.
20 Years on, newer insulations greatly increased the expected life of distribution transformers and 120 Volts was performing well.
That was the reason that appliances were rated at 112 Volts for 5 years, then 115 volts for 5 years and finally 117 Volts for 5 years.
Industrial voltages went from 440 Volts to 480 Volts, but I don't know the timetable. In some areas of Canada the industrial voltage is now 600 Volts.
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: History of secondary voltages in US
Another interesting thing that I have noticed is that when I buy incadescent lightbulbs they are 115 volt rated. With the power coming into my home is sometime about 120- 121 volts from the local transformer, these bulbs burn out often. But once and a while at discount stores we get a shipment of lightbulb from Canada and they are 125 volt rated and last longer. That's enough of my rant, interesting stuff.
Doug
RE: History of secondary voltages in US
I don't think it really "inch up" on purpose, what i recall reading somewhere was that there originally were NO standards. Early electricity providers, also being forced to be appliance mfrs in the early days as well, each created their own voltage level standards, most likely to aid in the perception of the as yet ignorant public that they had to stick with one source.
I believe it was the REA in the 30s that finally established standards and compromises. I've read a history of the REA, that's where I believe I got these concepts. I've also read a history of ANSI, but it was not specified to voltage levels, just saying which previous standards organizations went into creating ANSI standards, which are what we use now, but from that I think you can research the electrical predecessors for those standards and the REA program is in there.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: History of secondary voltages in US
I also noticed the early street cars used 600 V DC, and this was because of the DC motors. But many different cities used very different voltages for there street cars (mostly DC).
The history is very interesting because it gave us places names like Battery Park (guessing it came from the old Edison plant).
RE: History of secondary voltages in US
RE: History of secondary voltages in US
Without giving details, there once was a lake that was made to cool a powerplant. The plant is no longer there, but the lake remains. I am sure there are other monuments to the power industry.
You can't discuss distribution voltages without discussiong two phase electricity, and the Scott-T transformer to convert three phase to two phase.
RE: History of secondary voltages in US
So it appears that because of the fact that the crews were sent out with identical packages to be installed in rural farms, they settled on 230V (and thereby 115V) as the standard. The REA took the rural farm users from less than 11% electrified in 1934, to over 50% by 1942 and almost 100% by 1952; that was a LOT of systems installed in a short period of time. I read one article that said they electrified over 228,000 farms in 1939 alone. The ANSI standard is now 115/230V, so I'm sure the weight of the REA efforts over a very broad area drove the market to adopt this.
"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)
For the best use of Eng-Tips, please click here -> FAQ731-376: Eng-Tips.com Forum Policies
RE: History of secondary voltages in US
RE: History of secondary voltages in US
So, with "d" meaning distribution and "u" meaning utilization, the "modern" voltages are:
480V-d => 460V-u
240V-d => 230V-u
120V-d => 115V-u
d/u = 1.043
For the "older" equipment, say from the 1970's (or maybe 1960's, I'm not sure where the line was drawn) back to the 1940's, the voltages were rated differently. I do not have any direct experience with equipment older than 1939 so I cannot comment on that (for the record, I saw "1939" last month). The "older" voltages are:
460V-d => 440V-u
230V-d => 220V-u
115V-d => 110V-u
d/u = 1.045
For medium voltages:
2400V-d => 2300V-u d/u = 1.043
4160V-d => 4000V-u d/u = 1.040
6900V-d => 6600V-u d/u = 1.045
I do not claim the above information to be all inclusive. My experience is with motors in the US at 60hz.
RE: History of secondary voltages in US
Edison originally planned everything for 100 V DC -generators,light bulbs.Then after putting up his first line in Manhattan, he found the customers at the fag end of line complaining of poor illumination, obviously due to voltage drop.As bulbs were already made, he could not derate them for 90 V.The easiest thing he could do was to increase the generator voltage to 110V increasing the field excitation. Thus 110 V became standard,leading to 220V ,440V etc and later to 11,22,66,110,220 kV.
First AC power generation at Niagra was 2 phase as Tesla thought that be the simple solution.During stage one,power reached up to Buffalo.But when lines are to be extended to Newyork,developments in Europe caused a huge increase in copper prices and the directors of power company found that line cost will not justify extension to Newyork.Then Tesla mathematically found that three phase lines take the minimum copper for a certain amount of power to be transmitted.As pushed to wall and fearing loss of job, chief engineer of the project Mr Scott invented the brilliant idea of converting two phase to three phase by transformer connections.
RE: History of secondary voltages in US
RE: History of secondary voltages in US
RE: History of secondary voltages in US
Not all manufacturers or suppliers followed the standards in the early days. As part of the inching up process, I have seen household appliances rated at 110V, 112V, 115V, 117V and finally 120 Volts. That was long ago!!
Bill
--------------------
"Why not the best?"
Jimmy Carter
RE: History of secondary voltages in US
Next major Voltage standardisation effort was in 1927 at AIEE winter meeting on Feb7-11 at New York. See "Voltage standardisation of A C systems from view point of the Electrical Manufacturer" by F C Hanker(Westighouse) and HR Summerhayes(GE) AIEE pages 161-172.There were three more papers on the subject at the meeting from Utilities and consulting engineers.These papers briefly covered the historical evolution of voltage ratings.
AEP engineers Philip Sporn and H P ST. Clair published "A proposal for International Standardisation of EHv Transmission voltages" in AIEE June,1960.Pages281-284.This paper also covers the historical development of voltgae ratings in US
The current situation is covered by ANSI standard C84.1-2011 " Voltage Ratings (60 Hertz) for Electric Power Systems and Equipment"
Development of frequency rating in US is covered by "Frequency" -D B Rushmore AIEE 1912, pages 955-972 and "The Technical Story of the frequencies" B G Lamme AIEE 1018,Pages 65-89.