How does RISA calculate a Distributed load?
How does RISA calculate a Distributed load?
(OP)
I have mainly been in Land Development, but due to the economy I am trying to diversify and learn RISA 3D. I was trying to verify a result from RISA 3D. I just applied a load of 0.06 kips/ft to a beam 20 feet long with pinned connections. Per my 98 second edition LRFD Steel Design Manual, I had calculated that the moment(M) should be:
M=(wl^2)/8. So I would get M=(0.06 kips/ft*(20ft)^2)/8, which should equal -3 ft kip.
However, RISA calculates a value that is close, but not close enough for me. It calculates the Moment to equal -1.392 ft kip.
Can someone explain to me how it is calculating this value?
M=(wl^2)/8. So I would get M=(0.06 kips/ft*(20ft)^2)/8, which should equal -3 ft kip.
However, RISA calculates a value that is close, but not close enough for me. It calculates the Moment to equal -1.392 ft kip.
Can someone explain to me how it is calculating this value?
RE: How does RISA calculate a Distributed load?
I would recommend either sending your model into RISA tech support, or posting here on this forum.
RE: How does RISA calculate a Distributed load?
RE: How does RISA calculate a Distributed load?
Mike McCann
MMC Engineering
http://mmcengineering.tripod.com
RE: How does RISA calculate a Distributed load?
In this sort of situation, the total difference between positive and negative moment should equal WL^2/8. In your case the w is actually 0.0701 k/ft (that includes the applied self weight of the beam). So, we're looking for the total moment to be 3.505 k-ft
RISA gives 2.126 k-ft at the column support and 1.378 at mid-span. = 3.504 k-ft total. That should be within a reasonable round-off error.
RE: How does RISA calculate a Distributed load?